Dear Folks,
Can Smart UPS provide the power to the load when it is off or in fault?
Can Smart UPS online provide the power to the load when it is off or in fault ?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:29 AM . Last Modified: 2024-03-07 11:02 PM
Hi Rico
If there is utility power to the UPS then it is functioning, the output can be switched off but the UPS will be on, so there isn't really a shutdown state when utility power is present.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:29 AM . Last Modified: 2024-03-07 11:02 PM
Hi
The Smart UPS online have a bypass feature, so as long as utility power is ok then it can provide power if the UPS has issues.
The Smart UPS are a line interactive topology and do not have a bypass feature, so will not provide power if the UPS has an issue.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:29 AM . Last Modified: 2024-03-07 11:02 PM
Dear Matt,
thank you for your reply.
When the Smart UPS online is in shutdown state, can the utility power pass through it to the load ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:29 AM . Last Modified: 2024-03-07 11:02 PM
Hi Rico
If there is utility power to the UPS then it is functioning, the output can be switched off but the UPS will be on, so there isn't really a shutdown state when utility power is present.
Regards
Matt