Smart-UPS RT 5000 XL - Bypass not in range ; high voltage.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 XL - Bypass not in range ; high voltage.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
4
2457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

Smart-UPS RT 5000 XL - Bypass not in range ; high voltage.

Hello everyone,

I am getting email notifications every 2 mins for the past hour saying:

UPS: Bypass not in range ; high voltage.
I did get this one time.
Informational - UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.

I looked online and most of the issues were due to people having the Input voltage set higher than the output voltage.
I don't think this is my scenario.

Data Log
  Smart-UPS RT 5000 XL
Date  Time  Vmin  Vmax  Vout  Iout  %Wout  %out  FrqOut  %Cap  Vbat  Tups 
 01/05/2020   14:31:11   248.42   252.23   240.06   4.94   31.69   23.76   60.00   100.00   218.50   +75.88 
 01/05/2020   14:21:11   250.02   252.05   240.00   4.97   31.48   24.03   59.98   100.00   218.56   +75.88 
 01/05/2020   14:11:11   250.03   251.95   240.16   4.59   28.88   23.66   60.01   100.00   218.59   +76.55 
 01/05/2020   14:01:11   249.69   252.19   240.06   5.03   32.11   24.24   59.99   100.00   218.53 

 +75.88 

This is a screen cap of the data log.
I did attach the full 8 hours of data to this post.

01/05/2020 14:28:52 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
01/05/2020 13:16:36 Device UPS: Bypass not in range ; high voltage. 0x020F

I am not really sure how to fix this issue. For now, I just turned off the email notifications.
Any help you can provide would be excellent.
Thank you!

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:29 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
0
2452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:29 AM . Last Modified: ‎2024-03-07 11:02 PM

Thank you very much for your reply.
I will run through the logs later today and see what would be the appropriate settings.

Thank you again!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
0
2452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

Hi Chuck - 

From the NMC web interface go to "Configuration", then "Power Settings"

From here you can set the upper and lower bypass thresholds. The lowest setting for the upper limit is 252v, and from your logs it looks like you are hitting that pretty frequently. Raising the upper threshold should eliminate the nuisance alarms.

 

Thanks,

Liam 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
0
2452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

Hello Liam,

KKUUtMKUlpwV8DpdgmLb%2Fg%3D%3D.pngKKUUtMKUlpwV8DpdgmLb%2Fg%3D%3D.png

This is the current setup.
What would you recommend setting the Bypass Upper Voltage to?

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
0
2452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:28 AM . Last Modified: ‎2024-03-07 11:02 PM

Best bet would probably be to look through your data logs and see what the highest input voltage is, then set it to a few volts higher than that. something like 260v or 262v would likely be sufficient.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:29 AM . Last Modified: ‎2024-03-07 11:02 PM

0 Likes
0
2453
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:29 AM . Last Modified: ‎2024-03-07 11:02 PM

Thank you very much for your reply.
I will run through the logs later today and see what would be the appropriate settings.

Thank you again!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore