Hello All,
We have 2 UPS in parallel configuration on a location. Recently both the UPS just shutdown itself as well as the load, however just before the shutdown following alerts were received from UPS. we had 2 instances of UPS complete shutdown within 36 hours.
Device UPS: The external Switch Gear Q004 has opened.
Device UPS: The output power is turned off.
Device UPS: In bypass in response to an internal hardware fault.
Device UPS: Return from bypass, internal hardware fault no longer present.
Device UPS: In bypass in response to an internal hardware fault.
On First Instance found as below;
UPS was totally Shutdown & No Display.
The MCB supplying mains input power to UPS were tripped.
On Second Instance
UPS was totally Shutdown & No Display.
We would like to have your expertise for the below queries;
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:46 AM . Last Modified: 2024-03-19 01:52 AM
Hi,
You should contact local support for assistance. They will require logs and help you troubleshoot the issue. You will find local support contact information at this link
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 02:46 AM . Last Modified: 2024-03-19 01:52 AM
Hi,
You should contact local support for assistance. They will require logs and help you troubleshoot the issue. You will find local support contact information at this link
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.