Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS SUA3000RM2U Online light will not stay on

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SUA3000RM2U Online light will not stay on
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
7
2157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

Smart-UPS SUA3000RM2U Online light will not stay on

We have 5 of the Smart-UPS SUA3000RM2U, all of a sudden on one of them.  The "online" light goes off and the unit switches to battery power.   (power is good) plugged another UPS in the same receptacle and it works.  

So we replaced the batteries with a new battery pack.   But now the unit will not start via a power on, but it will start from a cold-boot. However, the online light flashes  six times then switches to battery. 

The L5-30R has 120 volts.  When I run the self test or try to power it on,  Here's what happens. 

1. Press power on - one quick beep - No power 

2. Tried Cold start,   released after beep - unit battery indicators full (with the old batteries) - (new battery pack shows half full)

    Online LED blinks six times - Then orange light "on battery" comes on. 

3. Hold for self-test - Remove battery unit powers on but Does the Same as #2 

4. network cards has solid green and flashing orange but still can't connect via IP Address. 

5. Unit does have output power , but it's using battery. 

Not sure what could be happening , it sounds to me that  unit is not getting power . 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

Hello Duane, I do apologize for the delayed response, but we do not typically check the forums on the weekends, and yesterday was a holiday in my home (and current) state of Rhode Island (Victory over Japan day, yes we still celebrate it).

Based on what you mention it looks like the UPS is operating correctly, able to power up and run on battery, but it is not able to go online and utilize incoming utility power. It looks like you verified that the outlet is working, from putting another UPS. 

Have you checked the input circuit breaker on the back of the unit? It should be very close to where the power cord enters the unit, and it might be popped out. If it is, please reset it by pushing it in, until it clicks. If you cannot get a click, then it has not tripped

If the circuit breaker is not tripped, and you are still unable to get power, I would inspect the power cord for any issues. It could have a loose connection or be damaged. In either of those cases, you would most likely have to replace the unit.

That being said, these units do typically have a lifespan of 5-7 years, based on the different electronic components inside, and there might be an issue with the UPS itself.These units have been discontinued for quite some time and it is most likely in that age range or older.  Again, in this occasion it would also have to be replaced. 

I acknowledge that especially for a non-profit, cost can be an issue. I would advise that you call into sales at 800 800 4272 and inquire about or Trade Ups program, where you can get a significant discount by trading in your old unit, and we will even cover the shipping cost of sending it back to us. 

Thanks, 

Shanon

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

No comments? or No Clues? or just Sorry out Luck? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

Staff do not work weekends.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

I'm neither of terribly knowledgeable about these larger units nor am I affiliated with APC/Schneider in any way. My only thought would be to try what is called a "braindead" on the unit: safely power down any attached load, turn the UPS off, disconnect both the batteries and AC line power. Then depress the power on button for a few seconds. The unit should flash its lights, click the relays and beep. When it has done so, this should clear the microcontroller's volatile memory. (No customized settings should be lost.)

Reconnect the battery, restore power and see if the unit is any happier.

It's definitely odd that the network management card wouldn't start up normally. If you have a 940-0024 communications cable, you might try hooking up a computer with terminal emulation software (2400/8/N/1, no flow control per default) to see if there is any response from the network card before you attempt the "braindead" procedure above.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

I would check the back of the unit for a circuit breaker. Sometimes they appear like round push pins.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

Yes, its seems strange to me.    I believe it's something  relative to the inverter?  this unit does have a breaker switch that I can see. there are rest buttons on the output  panel, which I have pressed many times.  

I went through the "Braindead" procedure, afterwards the unit powered on.  But the battery light nor the online light comes on.  Only three battery indicators.

The NIC has a solid green and a blinking orange light, seems like it communicating.   However, after numerous resets of the NIC card the MAC does not appear on our network.  

I don't have the original cable for some reason our network cabling guys throw them out.     

I hear a loud click when I press the power button.   But nothing happens, it only comes on when I do a cold start but the online light never comes on. 

These unit are old and they have served us well.   I guess we'll just put the new batteries in another unit.  

We're non-profit so anything we can do to save a little always helps. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2153
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

Hello Duane, I do apologize for the delayed response, but we do not typically check the forums on the weekends, and yesterday was a holiday in my home (and current) state of Rhode Island (Victory over Japan day, yes we still celebrate it).

Based on what you mention it looks like the UPS is operating correctly, able to power up and run on battery, but it is not able to go online and utilize incoming utility power. It looks like you verified that the outlet is working, from putting another UPS. 

Have you checked the input circuit breaker on the back of the unit? It should be very close to where the power cord enters the unit, and it might be popped out. If it is, please reset it by pushing it in, until it clicks. If you cannot get a click, then it has not tripped

If the circuit breaker is not tripped, and you are still unable to get power, I would inspect the power cord for any issues. It could have a loose connection or be damaged. In either of those cases, you would most likely have to replace the unit.

That being said, these units do typically have a lifespan of 5-7 years, based on the different electronic components inside, and there might be an issue with the UPS itself.These units have been discontinued for quite some time and it is most likely in that age range or older.  Again, in this occasion it would also have to be replaced. 

I acknowledge that especially for a non-profit, cost can be an issue. I would advise that you call into sales at 800 800 4272 and inquire about or Trade Ups program, where you can get a significant discount by trading in your old unit, and we will even cover the shipping cost of sending it back to us. 

Thanks, 

Shanon

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

0 Likes
0
2154
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:38 PM . Last Modified: ‎2024-03-06 11:53 PM

No Problem.   I wasn't really expecting an official response considering I posted this  Friday afternoon.  I was assuming this was an open forum and was really looking for others who may of had the same problem.  Like I said,  we have five of these and they have been good to us.   When you do good work, good things will happen.  A visitor was touring our Datacenter when he notice the UPS was powered off and we ran power from another rack.

He made a generous donation ,  and our CEO came by and thanked us.   She said , we do all we can with the small budget and these were some of the things that showed how hard we work.  

1

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore