Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Smart UPS SU1000RM2U not detected by NMC AP9617?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS SU1000RM2U not detected by NMC AP9617?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
BillP Leader
5060
voidstar_apc
voidstar_apc
196
Teken
Teken
164
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
12
5465
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Smart UPS SU1000RM2U not detected by NMC AP9617?

Hi,

Need help, if anyone know what is all about...

I have Smart UPS SU1000RM2U with Network Management Card AP9617

I'm using it to send  NMC   Info   to my QNAP server to shutdown when battery is on low level.

Everything work well till few days ago, when i noticed that UPS reporting  unusual  estimated remaining time on battery (160 or more HOURS, where real time is about 160 MINUTES).

I  Reboot-ed Management Interface thinking it will solve problem, but after that, i cannot se "UPS" tab within WebGUI.

When login with telnet, there is message:

"A UPS was found that is not supported by this application. Check CD-ROM for the correct application, or visit www.apc.com"

 Strange that everything is worked fine since last reboot???

Here is detailed information i got via telnet login: 

About System:

Model Number : AP9617
Serial Number : NA0741002680
Manufacture Date : 10/08/2007
Hardware Revision : A10
MAC Address : 00 C0 B7 CA EF D1
Flash Type : AMD A29DL322DB

-----------------------------------------------------------------------

Module Information

Description : Smart-UPS & Matrix-UPS APP
-----------------------------------------------------------------------
Name : sumx Type : StatApp
Version : 372 Sector : 16
Date : 02/02/2010 Time : 19:08:16
CRC16 : EFCA

Description : Network Management Card AOS

-----------------------------------------------------------------------
Name : aos Type : APC OS
Version : 373 Sector : 47
Date : 02/02/2010 Time : 17:05:14
CRC16 : B630

-----------------------------------------------------------------------

I tried flashing newest firmware to NMC card AP617 (file "apc_hw02_aos373_sumx372.exe"), with success, but without result i expected (still, NMC Web Interface can't see my UPS, and report estimated time on battery...)

Anyone know answer why I dont see "UPS" card on WebUI?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • a
  • ap9617
  • application
  • by
  • found
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

On 25/6/2017 12:08 AM, Nenad said:

Probably that's what I'm going to do. To bad that I changed batteries few months ago...

Pick up a replacement on E-bay or something and put the new batteries in that. SU series UPS are pretty common these days and pretty cheap secondhand with dead batteries. Still great and reliable units, except when they lose their minds. Doesn't seem to happen often, but your's is the third I've heard of (mine being the first).

You *could* try and re-set all the variables but you'd need a reliable AC RMS volt meter and a good power meter to re-calibrate it (if it is salvageable).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

I edited original post with more info. Can you ask concrete question (what info you expect)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Hi,

Is the serial cable attached to the UPS? If so remove it and restart the UPS. If not reset the UPS. You may also need to reset the NMC. 

To reset

1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back on

Reply

Link copied. Please paste this link to share this article on your social media post.

rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Hi Bill. Thank for your effort..

Tried everything in exact order, but without success. 

I also reseted nmc card, but also without success.

I can login via web and telnet, but could not get data from UPS. (ETA time, voltage, etc)

Any other idea?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Hi,

Telnet into the card and check the stats. They should read P+ N+ A+ If they do not try flashing the card again. If they read P+ N+ A+ then then try using a SNMP utility (I use PowerSNMP Free Manager) to see if the UPS and card are talking. Check something like Name: upsAdvInputLineVoltage Oid: 1.3.6.1.4.1.318.1.1.1.3.2.1 to see if the UPS is reporting the data. 

Reply

Link copied. Please paste this link to share this article on your social media post.

rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

About first part of question. When I login with telnet, I see stats P+ N+ A+

About second part of question, I don't know how to check these settings. I downloaded few SNMP Managers, and I-m currently learning how to read these data. Will report back ASAP

Reply

Link copied. Please paste this link to share this article on your social media post.

rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Hi Bill

I experimented with "ActiveXperts Network Monitor Manager" and I came to conclusion that UPS and card not talking.

I tried several OIDs from PowerNet-MIB (1.3.6.1.4.1.318.1.1.1.3.2.1  you suggested, and few others) and I didn't get any results.

Do you have any other suggestion?

In your opinion, will I get data if connect via serial cable? (Currently I don't have computer with serial port, so I must buy usb2 serial adapter)

Reply

Link copied. Please paste this link to share this article on your social media post.

rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

UPDATE:

Tried with terminal connection via serial cable (without NMC AP9617). Powerchute won't recognize it.

I got some strange readings. For example, when  I enter corresponding code in terminal, I got following ressults:

^A         Model: Smart-UPS 6 RM XL

m          UPS Manufacture Date: ÿÿÿÿÿÿÿÿÿÿ

z           Batteries Repalced date: ÿÿÿÿÿÿÿÿ

c           UPS ID: ÿÿÿÿÿÿÿÿ

n           Serial Number: ÿÿÿÿÿÿÿÿÿÿÿÿÿÿÿÿ

Furhther more, with apcfix.exe, got these results for Smart constants:

(4 5 6 0) FF FF FF 0B

Is this some kind of hardware failure?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
BillP Leader
Leader

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

Hi,

In order to use the UPS-Link language to communicate with the UPS, the character uppercase "Y" must be sent to the UPS when the UPS is turned on. The UPS will respond with the characters "SM". Did you enter Y before entering the other characters? If you did and you received the responses posted then the UPS communications is messed up and the unit should be replaced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

On 23/6/2017 5:18 PM, Nenad said:

Is this some kind of hardware failure?

Sounds like the eeprom in the UPS has lost its mind and it doesn't know what it is anymore. Unless you are *really, really* attached to it you should probably be looking for a replacement.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

Do you have a picture of the model number from the white sticker of the unit?

Reply

Link copied. Please paste this link to share this article on your social media post.

rassha_apc
rassha_apc
Explorer

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

Probably that's what I'm going to do. To bad that I changed batteries few months ago...

Here are pictures from white sticker with serial number

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Brad_C
Contributor

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

0 Likes
0
5464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:37 AM

On 25/6/2017 12:08 AM, Nenad said:

Probably that's what I'm going to do. To bad that I changed batteries few months ago...

Pick up a replacement on E-bay or something and put the new batteries in that. SU series UPS are pretty common these days and pretty cheap secondhand with dead batteries. Still great and reliable units, except when they lose their minds. Doesn't seem to happen often, but your's is the third I've heard of (mine being the first).

You *could* try and re-set all the variables but you'd need a reliable AC RMS volt meter and a good power meter to re-calibrate it (if it is salvageable).

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore