Excessive Charging Voltage for SURTD5000XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Excessive Charging Voltage for SURTD5000XLI
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
1
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

Excessive Charging Voltage for SURTD5000XLI

Can someone please advise if this is repairable, whenever I conduct PM to the UPS, I always check its charging voltage, and the range that I always get is from 215-219VDC. Now, when I tried to check the said UPS Model I had a reading of 235V DC which I think is too high for the charging of the UPS. How can I repair or rectify this concern with the UPS? Any help is much appreciated. Thank you. 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

hello,

Try out the following only at your own risk, I take no responsibility if something goes wrong. I tested this method only on SUA**** series of APC UPSes so I don't know if it works at all for SURTD.

Remove all accessories connected to the UPS (eg. Smart slot cards)

Connect with a terminal program to your UPS using the RS-232 port (not USB!)

The correct settings for the COM-connection are 2400 Baud, 8 data bits, 1 Stop bit, no parity, protocol Xon/Xoff. Make sure that the option FIFO activated is unchecked (if there is such option in your terminal program, that is). 

When the connection is established to the UPS, press Shift + Y (capital Y) the UPS should respond with 'SM'

Type 1, wait 1.5-3 secs and type 1 again (Should return 'Prog') 

Press Shift + B (capital B), UPS should respond with a hexadecimal value (write it down so if something goes bad you can reset it to this value)

Press + or - sign to increment/decrement the value, and the charger voltage should change. It *might* happen that the voltage detected by the UPS remains the same, but the voltage measured at the battery terminals do change (false battery voltage reading). You can't do anything about this, it is either high charging voltage and accurate battery voltage reports, or adjusted charger voltage and inaccurate readings.

Press Shift + R (capital R) to close the session, UPS should respond 'BYE'

Close the terminal.

Please note that these steps modify things inside the EEPROM, so it is a very delicate matter. Do this only if you really must, otherwise take the unit to trained service personnel for repairs.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

0 Likes
0
708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:12 AM . Last Modified: ‎2024-03-18 02:38 AM

hello,

Try out the following only at your own risk, I take no responsibility if something goes wrong. I tested this method only on SUA**** series of APC UPSes so I don't know if it works at all for SURTD.

Remove all accessories connected to the UPS (eg. Smart slot cards)

Connect with a terminal program to your UPS using the RS-232 port (not USB!)

The correct settings for the COM-connection are 2400 Baud, 8 data bits, 1 Stop bit, no parity, protocol Xon/Xoff. Make sure that the option FIFO activated is unchecked (if there is such option in your terminal program, that is). 

When the connection is established to the UPS, press Shift + Y (capital Y) the UPS should respond with 'SM'

Type 1, wait 1.5-3 secs and type 1 again (Should return 'Prog') 

Press Shift + B (capital B), UPS should respond with a hexadecimal value (write it down so if something goes bad you can reset it to this value)

Press + or - sign to increment/decrement the value, and the charger voltage should change. It *might* happen that the voltage detected by the UPS remains the same, but the voltage measured at the battery terminals do change (false battery voltage reading). You can't do anything about this, it is either high charging voltage and accurate battery voltage reports, or adjusted charger voltage and inaccurate readings.

Press Shift + R (capital R) to close the session, UPS should respond 'BYE'

Close the terminal.

Please note that these steps modify things inside the EEPROM, so it is a very delicate matter. Do this only if you really must, otherwise take the unit to trained service personnel for repairs.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of