Smart UPS SRT: parallelisation & disable outlet groups by default

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS SRT: parallelisation & disable outlet groups by default
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
4
791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Smart UPS SRT: parallelisation & disable outlet groups by default

Hi,

I am currently designing 2 interacting electrical cabinets, each having its own Smart UPS SRT 10000VA. Before freezing the design I have a couple of questions:

  1. Can the UPSs be put "in parallel" (connected by Ethernet, really) so that if one gets powered on/off by a dry contacts card, it will command the other to follow? Or should I need to allow additional signals for an addition dry contacts card to be commanded in the same way?
  2. Can specific outlet groups be set as disabled by default when powering on, and commanded to turn on later on through Ethernet?

Thank you in advance,

Kind regards

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Thank you both for your answers. It looks like I'll have to use a second dry contacts card then, this is to wire to emergency switches and bimetal switches so with relays I can make them isolated from eachother.

I am more bothered about the fact the outlet groups cannot boot in a predefined state no matter the shutdown cause, but I guess I will have to find another less convenient way to make sure my temperature controllers don't boot unsupervised before the PC. I'll leave that thread open for now.

Off topic: your website may be annoyingly slow to respond, but I must admit your forum is the best one I have seen in a while, congratulations.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Hi,

I am currently designing 2 interacting electrical cabinets, each having its own Smart UPS SRT 10000VA. Before freezing the design I have a couple of questions:

  1. Can the UPSs be put "in parallel" (connected by Ethernet, really) so that if one gets powered on/off by a dry contacts card, it will command the other to follow? Or should I need to allow additional signals for an addition dry contacts card to be commanded in the same way?
  2. Can specific outlet groups be set as disabled by default when powering on, and commanded to turn on later on through Ethernet?

Thank you in advance,

Kind regards

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Hello.

Here is what I know, also after consulting with our EMEA region support team.

1.) Parallel capability is not yet available for these units. I am not sure how it is going to work when it is released but I think it may require a hardware change when it is released. I imagine they might make a specific SKU for it. One option I know of to sync control commands would be using Sync Control option in the onboard Network Management Card. It uses multi-cast network technology and is designed to help sync up the controls between multiple UPSs so if you reboot one UPS, the other will also reboot at the same time. It is good for equipment with redundant power supplies. I don't know if that would suffice. Alternatively, you can add an AP9613 Dry Contacts SmartSlot card to each UPS for dry contacts (or an AP9810 dry contacts accessory - each UPS supports (1) by default - (2) inputs and (1) output are on each AP9810) but there is no way to tie them together as far as I know. I am not sure if you'd be able to wire the contacts themselves in parallel but it may be possible depending on what your dry contacts would be wired into.

2.) Yes, I see this as an available option for the outlet groups on an SRT.

2618_OutletGroup.png

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
0
789
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Something to be aware of: synch control groups act on the entire UPS, not at the level of individual outlet groups.

Also, "stay off after power returns" only applies when the UPS is turned off due to one of the load shedding conditions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

0 Likes
0
790
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:03 AM . Last Modified: ‎2024-03-12 01:23 AM

Thank you both for your answers. It looks like I'll have to use a second dry contacts card then, this is to wire to emergency switches and bimetal switches so with relays I can make them isolated from eachother.

I am more bothered about the fact the outlet groups cannot boot in a predefined state no matter the shutdown cause, but I guess I will have to find another less convenient way to make sure my temperature controllers don't boot unsupervised before the PC. I'll leave that thread open for now.

Off topic: your website may be annoyingly slow to respond, but I must admit your forum is the best one I have seen in a while, congratulations.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of