Smart UPS SRT: parallelisation & disable outlet groups by default
Hi,
I am currently designing 2 interacting electrical cabinets, each having its own Smart UPS SRT 10000VA. Before freezing the design I have a couple of questions:
- Can the UPSs be put "in parallel" (connected by Ethernet, really) so that if one gets powered on/off by a dry contacts card, it will command the other to follow? Or should I need to allow additional signals for an addition dry contacts card to be commanded in the same way?
- Can specific outlet groups be set as disabled by default when powering on, and commanded to turn on later on through Ethernet?
Thank you in advance,
Kind regards
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
Thank you both for your answers. It looks like I'll have to use a second dry contacts card then, this is to wire to emergency switches and bimetal switches so with relays I can make them isolated from eachother.
I am more bothered about the fact the outlet groups cannot boot in a predefined state no matter the shutdown cause, but I guess I will have to find another less convenient way to make sure my temperature controllers don't boot unsupervised before the PC. I'll leave that thread open for now.
Off topic: your website may be annoyingly slow to respond, but I must admit your forum is the best one I have seen in a while, congratulations.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
Hi,
I am currently designing 2 interacting electrical cabinets, each having its own Smart UPS SRT 10000VA. Before freezing the design I have a couple of questions:
- Can the UPSs be put "in parallel" (connected by Ethernet, really) so that if one gets powered on/off by a dry contacts card, it will command the other to follow? Or should I need to allow additional signals for an addition dry contacts card to be commanded in the same way?
- Can specific outlet groups be set as disabled by default when powering on, and commanded to turn on later on through Ethernet?
Thank you in advance,
Kind regards
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
Hello.
Here is what I know, also after consulting with our EMEA region support team.
1.) Parallel capability is not yet available for these units. I am not sure how it is going to work when it is released but I think it may require a hardware change when it is released. I imagine they might make a specific SKU for it. One option I know of to sync control commands would be using Sync Control option in the onboard Network Management Card. It uses multi-cast network technology and is designed to help sync up the controls between multiple UPSs so if you reboot one UPS, the other will also reboot at the same time. It is good for equipment with redundant power supplies. I don't know if that would suffice. Alternatively, you can add an AP9613 Dry Contacts SmartSlot card to each UPS for dry contacts (or an AP9810 dry contacts accessory - each UPS supports (1) by default - (2) inputs and (1) output are on each AP9810) but there is no way to tie them together as far as I know. I am not sure if you'd be able to wire the contacts themselves in parallel but it may be possible depending on what your dry contacts would be wired into.
2.) Yes, I see this as an available option for the outlet groups on an SRT.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
Something to be aware of: synch control groups act on the entire UPS, not at the level of individual outlet groups.
Also, "stay off after power returns" only applies when the UPS is turned off due to one of the load shedding conditions.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:03 AM . Last Modified: 2024-03-12 01:23 AM
Thank you both for your answers. It looks like I'll have to use a second dry contacts card then, this is to wire to emergency switches and bimetal switches so with relays I can make them isolated from eachother.
I am more bothered about the fact the outlet groups cannot boot in a predefined state no matter the shutdown cause, but I guess I will have to find another less convenient way to make sure my temperature controllers don't boot unsupervised before the PC. I'll leave that thread open for now.
Off topic: your website may be annoyingly slow to respond, but I must admit your forum is the best one I have seen in a while, congratulations.