Smart-UPS SRT 5000 (ID1013) FW Update from 15.0 to 15.3 refused

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SRT 5000 (ID1013) FW Update from 15.0 to 15.3 refused
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
TUDD
TUDD
Cadet

Posted: โ€Ž2025-08-19 07:38 AM

0 Likes
5
549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-19 07:38 AM

Smart-UPS SRT 5000 (ID1013) FW Update from 15.0 to 15.3 refused

Hello,

my UPS device seems to be bricked.

 

Update with Firmware Upgrade Wizard 4.3.8 using USB don't work.

Update with Firmware Upgrade Wizard 4.3.8 using COM1 don't work.

Update with Network Management Web Interface using HTTP don't work.

Update with Network Management Web Interface using HTTPS don't work.

Update with Command Line using SSH don't work.

 

apc>upsabout
E000: Success
Model: Smart-UPS SRT 5000
SKU: SRT5KXLI
Serial Number: AS2036271158
Firmware Revision: UPS 15.0 (ID1013)
Manufacture Date: 02.09.2020
Apparent Power Rating: 5000 VA
Real Power Rating: 4500 W
Battery SKU: APCRBC140


apc>cd tmp
E000: Success

apc>dir
E000: Success
0 Aug 31 2020 ./
0 Aug 31 2020 ../
1416064 Aug 19 15:24 SRT1013UPS_15-3.enc

apc>upsfwupdate -install -file "/tmp/SRT1013UPS_15-3.enc"
E100: Command Failed

apc>upsfwupdate -lastresult
E000: Success
Last Update Result: Refused

apc>upsfwupdate -info -file "/tmp/SRT1013UPS_15-3.enc"
E000: Success
Update File: /tmp/SRT1013UPS_15-3.enc
Compatible with UPS: Yes
Update Version: ID1013UPS 15.3

apc>_

 

How can I solve this problem?

 

Thanks and best regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-08-19 11:34 PM

0 Likes
4
547
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-19 11:34 PM

Are you using the supplied RJ50 - RS232 Serial cable and the FUW?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

TUDD
TUDD
Cadet

Posted: โ€Ž2025-08-19 11:37 PM

In response to Teken
0 Likes
3
539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-19 11:37 PM

Yes, of course. I don't need any RS232 serial cable for SSH/HTTP/HTTPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-08-20 04:56 AM

In response to TUDD
0 Likes
2
534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-20 04:56 AM

Your reply is still not clear so will rephrase the question. Are you using the supplied APC RJ50 - RS232 Serial Cable to connect directly and communicate with the target device?!?

 

Updating the UPS Firmware any other way is a disaster waiting to happen and will result in a bricked system.

 

So to be crystal clear do not attempt to flash update the UPS Firmware using the NMC, USB!

 

What is the current state of the system now? Is it still fully operational or is the LCD blank or is none responsive?!?

 

Provide a photo of the LCD and what is displayed.

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

TUDD
TUDD
Cadet

Posted: โ€Ž2025-08-20 08:21 AM

In response to Teken
0 Likes
1
528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-20 08:21 AM

According to the release notes of firmware SRT1013, changes to protect the UPS firmware code have been implemented in version 15.0. Is this the reason why all network-based methods are no longer supported?

 

Current state: The UPS operates without any detectable errors.

 

The supplied cable consists of an RS232 socket (9 pin) and a jack plug (3 pin). This connection basically works, but firmware updates are not possible. The same behavior occurs as with SSH.

 

Thanks for any advise.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2025-08-21 04:07 AM

In response to TUDD
0 Likes
0
511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2025-08-21 04:07 AM

Yes, all network serial related connections has been disabled until either the interim firmware or last release is installed.

 

Once installed the following ports can be enabled / disabled based on user needs: USB, NMC, Serial via the LCD Menu.

 

Suggest you use the LCD Menu to see if this option is available and enable serial connection to the RJ50 port.

 

If the toggle option is not present than this RJ50 port should still be active and enabled for direct communications.

 

As a reminder, all other connections must be removed including the NMC from the system as outlined in the APC Firmware FAQ.

 

Meaning no USB connection to PCSS, PCBE, etc. NMC is hot swappable so you can just remove the two screws and eject. If the NMC is embedded than simply disconnect the Ethernet cable from the NMC.

 

Only connection should be to a dedicated laptop properly configured per the APC FAQ. Wired directly to the laptop and on the back of the RJ50 Serial Port.

 

NOTE: Some units have a RJ45 Port that is / was covered by a black plug. This is (NOT) the Serial Port but was intended for other future use and is not active.

 

Verify youโ€™re not using this port . . . โ˜๏ธ

 

Questions Ask . . . ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore