Smart-UPS SMT2200I halved expected runtime

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SMT2200I halved expected runtime
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
125
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
5
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

Smart-UPS SMT2200I halved expected runtime

Hi APC,

I purchased an SMT2200I a week ago, I notice that it only shows half of the expected runtime in a given load according to the chart on the APC website. I have done the following:

1. Researched on similar issues, one very similar I found HERE, tried the suggestions, didn't work.

2. Letting it charge for at least 24 hours

3. Self-Test

4. Runtime Calibration (at 100% charge, at 32-35% load so within +/-5%, and let it recharge for 24 hours afterwards)

5. Upgraded firmware (was 9.3, now 9.4). The initial reason I upgraded the firmware was because my SMT2200 fan wouldn't stop spinning even several hours after it charged to 100%. Several mins full speed spin, then low speed for about 10 seconds, then back to full speed for several minutes, repeat forever. After upgrading to 9.4, it seems to be fine.

6. Manual calibration after 24 hours on charge, then drain the UPS with 33-35% load till it switched off, followed by another 24 hour recharge

Currently the UPS is showing showing:

OnLine, Green Mode, 100% battery, 54.5V battery, 277W, 52 minutes.... whereas according to the chart, I should be seeing 109 mins

This halved runtime has not changed after calibrations, didn't improve, didn't get worse.

Eventhough I purchased this a week ago, I can see on the UPS test receipt, it Passed all tests on 08/06/2016. So basically I have purchased a UPS that has been on the shop's storage for at least a year (could be 8th of June, could be 6th of August 2016). Would the batteries have degraded in that period eventhough they were not attached?

Thank you for your help.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

Yeah, I expected the voltage to drop, thought I put that info in anyway in case it leads to other things.

I've re-flashed the latest firmware, and performed Factory Reset, still no change.

Shame that I paid for an SMT2200 but performs like an SMT1500.

Another annoying thing is one of the four metal clips that hold the door for the batteries already broken on the 2nd day. The battery door hangs slightly out now due to that.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

If they deeply discharged they will go bad, if they had more than 25% when you got them they should be fine. You really should phone support as they can action a solution on the spot, ie send a new battery pack if they deem yours faulty. They would cross ship so you get the new then send the old.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

The batteries had plenty of charge when I purchased the UPS, because we power-up tested it. It was around 60-70% I think, can't remember exactly.

I guess I can try calling them up, but thought I try here first in case there is a solution. I'm located in Jakarta, Indonesia, doubt they have a cross-ship service.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

I will try to keep adding bits of information/findings as I go along.

While the batteries reach 54.5V after 24 hours of charging, as soon as I run a test, voltage will drop to 52.1V.

I'm a bit reluctant to perform calibrations too often as I read somewhere performing calibrations should be done once every 6 months. I've done several calibrations in the past week I worry that the battery will degrade much quicker.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
975
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

The drop in voltage is normal due to the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

0 Likes
0
976
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:27 AM . Last Modified: ‎2024-03-18 01:30 AM

Yeah, I expected the voltage to drop, thought I put that info in anyway in case it leads to other things.

I've re-flashed the latest firmware, and performed Factory Reset, still no change.

Shame that I paid for an SMT2200 but performs like an SMT1500.

Another annoying thing is one of the four metal clips that hold the door for the batteries already broken on the 2nd day. The battery door hangs slightly out now due to that.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of