Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS SMT1000I strange behaviour

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS SMT1000I strange behaviour
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
7
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Smart-UPS SMT1000I strange behaviour

Hello to all.

I'm here to share my experience with this APC's product and, mainly, have your opinion about

I bought it last November 2013, everything works fine until one month ago:

Suddendly, without any reason, all the Group 1 outlets went OFF. The Others outlets were OK (tested). I had to manually switch the UPS completely OFF and then back ON to resume everything to the original conditions

As soon as I had all my peripherals back ON (this issue switched brutally OFF my two PCs, modem, monitor, etc.) I checked the eventlog and I found:

"11/09/14 23:19:55 Outlet Group 1 commanded to: turn off using delay

11/09/14 23:19:55 Shutdown process started

11/09/14 23:19:55 Battery Discharged

11/09/14 23:19:55 Online (Green Mode) - Exited"

On datalog instead:

Date and Time    Maximum Line Voltage    Minimum Line Voltage    Line Voltage    Output Voltage    Battery Voltage    Output Frequency    UPS Load    UPS Internal Temperature    Probe 1 Temperature    Probe 1 Humidity    Probe 2 Temperature    Probe 2 Humidity    Input Frequency    Battery Capacity

"11/09/2014 23:05:43    N/A                                    N/A                     230,4                 230                     27,2                    50,0                    29,9                   29,7                                    N/A                        N/A                         N/A                            N/A                      50,0                     100

11/09/2014 23:30:18     N/A                                    N/A                     230,4                 230,4                   27,2                   50,0                    31,8                   29,7                                     N/A                        N/A                         N/A                            N/A                      50,0                     100

So, if in the datalog everything is fine, what started the events showed in the previous log?

Of course I have already contacted APC Customer Support and they offer me a replacement. Ok, I said to myself, wonderful!

But everything is shining is not always gold....

The device received was a refurbished one, Ok, I can survive if it works as stated.... BUT, unfortunately, the upper case is not in perfect conditions and the front panel doesn't stay attached correctly.

I finally refuse that device and I kept my original one, the Customer Support request me some photoes and they decide to send me another replacement, never received

Now, yesterday I check, found it possible and did a firmware upgrade of my UPS, resetted both eventlog and datalog entries and now I'm monitoring it, but a particular entry make me curious:

10/12/1401:22:16Monitoring Started
10/12/1401:22:19Communication Established
10/12/1401:21:22

Monitoring Stopped

Also before the firmware upgrade there were a lot of entries like those ones, anyone can tell me if it's normal or not?

Actually those three are the only ones present in the eventlog since yesterday, after the firmware upgrade

Tks in advance!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

I'm glad to hear. Thanks and same to you!!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

In PowerChute Business Edition, my first guess would be that the Batteries Discharged event was configured to start a shutdown of the system/UPS. Batteries Discharged would typically appear if you have low runtime - whether because of an older battery or a battery that was exhausted after a power outage. The two lines of the data log don't help a lot because they are also far apart (per the timestamps). Can you check the Event Action configuration for Batteries Discharged? And how much runtime does your UPS report as available with the load attached?

Monitoring Started/Stopped is explained in the help file and user's guide. It refers to when the PowerChute Business Edition agent service was stopped or unable to monitor the UPS. If it is happening frequently, we'd usually see if you're using USB or serial and see if we can pinpoint it to the UPS or the computer you're using. It can also happen in expected situations such as when you reboot your computer (and thus the PowerChute service), when the UPS is rebooted, and a few other times. From what you said, it sounds like it was happening frequently.

Ideally, we'd want to see the full logs to see the history of the unit to investigate further.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Tks for your reply

I pasted just two datalog entries because, I think, they should be enough to understand there is something crazy. Here what I mean:

With that load the UPS, in normal conditions, report always a runtime remaining not less than 39 minutes

So, if you compare the datastamps in the two logs:

HOW can be possible that the battery from 100% of its capacity goes to minimum in 14 minutes?

HOW can be possible the battery is back fully charged in 11 minutes (100%)?

The settings were to initiate the switch off procedure 180 seconds at runtime limit, but why the Group 1 outlets only? The settings are valid for all the outlets

The settings were to switch back the outlets ON as soon as the main power returns, but the power was not missing at all!

So, as you can suspect, the questions became a lot.

I bought that UPS via Trade online APC website, is possible that it's not brand new? Uhmmm....

The battery was connected in the middle of November 2013, just after I unbox the UPS, connected to the electrical house plug without any load for more hours than the requested by the installation manual

Are they able to sell a new UPS with an old battery?

The computer where the UPS is attached is ON 365 days per year, it reboot just one time per month, after the MS updates, but having a look in the event log seems that it reboots at least one time per week.

The PC and UPS are connected via USB, the serial port can't be considered at all because the modern PCs born without it, also as a plug on the motherboard, you can't find it

Now the logs entries are resetted, firmware upgraded and I'll wait to see.

I attach now the eventlog involved, the same I sent to the Customer Support, just to make you smiling smile

For sure I learned a main lesson: never buy from an APC's store, I'm using APC since years, for me and parents, never a problem, this time was the first one I choose an APC shop and these are the results. Wow!

About the Customer Support, let me to shut up, is better

Tks again for your time, I'll keep you informed about any news


Attachments
EventLog.txt.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Hi again,

I will see about having someone more senior reach out to you from our EMEA support region. There are a few possibilities here that might be better explained in detail offline regarding why Batteries Discharged may have showed and maybe it is not the battery that caused the issue. Any units purchased via Trade-UPS, unless clearly specified as open box or refurbished would be new. Batteries are consumable items and can also have manufacturing defects sometimes and not hold their capacity or function as they should. I see what you mean in the log on how there was no Power Failed message before the Batteries Discharged.

If the Battery was the case and it was under warranty and a problem was identified with it, it would be replaced under warranty. I am still unclear here exactly what happened though and am not convinced it is a battery if the UPS never went to battery so that is why I'd like to have someone reach out to you to work through it or review the support case you already started to make sure it is being handled efficiently.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Hello Mrs Angela and tks for your answer.

Right now I have mainly to understand why that PC reboots, I discover yesterday it reboots at 7:19 pm and today at 7:10 pm. There is something hidden to me in its settings.

For the UPS, I'll see the eventlog in the next days, if I'm lucky the firmware upgrade solve everything (I'm also convinced that it's not a battery problem)

Tks again for your time!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

After more than one year, seems that the PC connected to the UPS decide itself to set windows update to reboot after updates.... Now I did everything to stop it!!

For the rest..... no news, good news. No strange event recorded, it's like a baby sleeping... smile

I still wait before to organize a party, but the sensation is that I (not the customer support) fixed the issue with the firmware upgrade..... sssshhhhh, shutup Andy! laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1573
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Hellooooooo

Finally, after about nine days after the firmware upgrade, still there aren't no entries in the eventlog.

Checking the old one I attached to my previous post, between each daily entry there is a minimum of one day up to a maximum of six days.

By my side, after nine days with no entries at all, I can surely affirm that the UPS is finally enjoying a new life!!!

So, at this point, I don't have any more questions.

Tks again for your time and support, very appreciated!!!

Have a nice time and I wish you a merry Christmas and a best new year!!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

I'm glad to hear. Thanks and same to you!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore