SMART-UPS RT 8000 - How to find out which battery is bad.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMART-UPS RT 8000 - How to find out which battery is bad.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
5
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

SMART-UPS RT 8000 - How to find out which battery is bad.

We have a SMART-UPS RT 8000 (SURT8000RMXLT6U) that is showing a bad battery. Is there a way to find out exactly which module needs to be replaced ?

I cannot find anythin from the web interface.

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • replacement
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
2916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Hello,

Do you have external battery packs? This UPS itself contains (2) RBC44 batteries and each RBC44 comes with two modules/strings. If the UPS reports a replace battery alarm, then you'd need to replace (2) RBC44. If you have external battery packs, or want to just replace the specific string, we would not really support opening the modules to identify open cells, etc though I think people with in depth battery knowledge sometimes do that with the UPSs and proceed at their own risk. The UPS itself cannot detect this type of failure though and would just be able to tell you that the batteries need to be replaced. Assuming the batteries are older though, the recommendation is to replace all of them since they are the same age. Replacing some older with some newer would damage the newer batteries and is not recommended, though I understand it may be realistic due to cost sometimes.

Long story short, assuming this UPS/batteries, no matter how many are anywhere from 2-5 years and it makes sense that they are now in need of replacing (versus being a brand new install where batteries should not be failing), you'd want to replace all batteries in the system since they are all used equally and look like one giant DC battery bus to the UPS.

I hope that helps.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

0 Likes
0
2917
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 09:04 AM . Last Modified: ‎2024-03-12 01:17 AM

Hello,

Do you have external battery packs? This UPS itself contains (2) RBC44 batteries and each RBC44 comes with two modules/strings. If the UPS reports a replace battery alarm, then you'd need to replace (2) RBC44. If you have external battery packs, or want to just replace the specific string, we would not really support opening the modules to identify open cells, etc though I think people with in depth battery knowledge sometimes do that with the UPSs and proceed at their own risk. The UPS itself cannot detect this type of failure though and would just be able to tell you that the batteries need to be replaced. Assuming the batteries are older though, the recommendation is to replace all of them since they are the same age. Replacing some older with some newer would damage the newer batteries and is not recommended, though I understand it may be realistic due to cost sometimes.

Long story short, assuming this UPS/batteries, no matter how many are anywhere from 2-5 years and it makes sense that they are now in need of replacing (versus being a brand new install where batteries should not be failing), you'd want to replace all batteries in the system since they are all used equally and look like one giant DC battery bus to the UPS.

I hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

MichalP
MichalP
Cadet

Posted: ‎2025-09-21 07:08 AM

0 Likes
1
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-21 07:08 AM

I have similar question: 
I bought (4 packs) new battery modules and replaced them (I have an APC SURT 8000 RM XLI + 1 External Battery Pack), and despite the replacement, I still have errors in the logs and a critical 'discharged battery' alarm in the web interface. How can I identify which battery module is faulty? I keep getting two messages in the logs: 
UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
UPS: A discharged battery condition no longer exists.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-22 04:27 AM . Last Modified: ‎2025-09-22 01:49 PM

In response to MichalP
1 Like
0
955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 04:27 AM . Last Modified: ‎2025-09-22 01:49 PM

You’ll need to provide a lot more information such as logs, history, and the systems environment.

 

Provide the following logs for review via Power Chute / NMC: Event, Data, UPS, Diagnostic.

 

There is no mention of completing any of the required action items during a RBC replacement.

 

The RBC must be allowed to fully charge before you attempt to complete these action items! ☝️

 

As such I’ll assume they are still outstanding so complete them now and report back the results with all logs called out up above.

 

Date: The battery installation date must be entered during a RBC replacement. Doing so resets internal counters and adjusts charging tables if applicable.

 

This can be done via Power Chute / NMC / CLI.

 

Self Test: Manually initiate a self test and let pass via the following methods: Panel, NMC, Power Chute.

 

Allow the RBC to return to 100% SOC before the next action item. If the self test fails report this outcome and stop and provide the active fault / error codes.

 

Battery Calibration: Manually initiate a battery calibration with a minimum of 30% attached load or higher. Once complete the system will reflect the operational runtime more accurately and learn the RBC state of health.

 

Allow the RBC to fully recharge to 100% SOC.

 

NOTE: Validate the system has been properly configured to know the number of external battery packs are present as outlined in the manual:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=SU_IOM_990_2689J_EN...

 

RBC: Using a calibrated DMM measure the float voltage for all individual RBC and document. Disconnect all of them and measure their initial charged voltage and document.

 

Leave disconnected for 72 hours and measure / document what the voltage is for the RBC pack.

 

Report back the values for all measurements here for review. 

Questions Ask . . . 👍

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

MichalP
MichalP
Cadet

Posted: ‎2025-09-22 11:48 PM

0 Likes
1
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-22 11:48 PM

The battery replacement instructions are concise and for the SURT8K model, they are limited to disconnecting the old modules and inserting the new ones, initiating a self-test in the NMC, and manually setting the replacement date in the NMC (And of course I did that). I have 1 External Battery Pack. I am attaching a few screenshots from the NMC; maybe they will help.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-09-23 03:48 AM

In response to MichalP
1 Like
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-23 03:48 AM

Are the four RBC APC originals, aftermarket, rebuild?!? Complete the measurements as outlined up above and report back the values here.

 

First measurements will be taken at the RBC connector(s) from the system to verify DC output voltage for each cartridge.

 

Proceed to connect one RBC back to the system and measure DC charging / float voltage for all packs and report back the values for each.

 

Complete the process by disconnecting all RBC. Measure the initial surface charge of each pack and record. Come back in 72 hours and report back the voltage for each pack.

 

The expectation is all individual packs will drop 0.1 - 0.3 VDC after the initial surface charge has dropped. If you see any RBC pack drop 1-3 VDC this indicates a potential fault.

 

Lastly, let’s just assume the RBC are all fine and healthy and using genuine CSB HR cells.

 

You can complete the battery calibration so the system can learn RBC SOC / Health. If there is an option to manually initiate a battery calibration via Power Chute / NMC do so.

 

If there is no option than you will need to perform a Lights Out / Grid Down test. Ensure there is 30% or greater load on the system and simply disconnect AC Mains from the system.

 

Allow the system to drain until it automatically shutdowns. If the system is connected to a computer running Power Chute disconnect this communication cable.

 

Obviously this should be completed during a maintenance window. Replace the loads with a heater that has a variable fan / heat setting to allow you to meet the minimum 30% or greater load.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore