Smart-UPS RT 8000 RM XL - without notice to PCNS clients? UPS: The output power is turned off due to a low battery.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 8000 RM XL - without notice to PCNS clients? UPS: The output power is turned off due to a low battery.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
125
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

0 Likes
6
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

Smart-UPS RT 8000 RM XL - without notice to PCNS clients? UPS: The output power is turned off due to a low battery.

Recently a digger had hit a ground power wire and in our area power was off for approx one hour.

Our Smart-UPS RT 8000 RM XL had only created this event:

     UPS: The output power is turned off due to a low battery.

No signal to the PCNS clients and consequently no planned shut-down behaviour has occurred.

This week-end I have tested the whole setup manually by just simply pulling out the power cord from the UPS. The intended event communication has started and all systems were properly shut-down after the configured amount of time.

Question: Why had the ups not worked as expected? What could we do to prevent hard power off event, when the UPS does not report itself the input power failure? Have we something missed?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

Hi Angela,

thank you for your quick reply and help. The log files are attached. The issue has happened on

23.05.2013    14:55:49    UPS: The output power is turned off due to a low battery.    0x0114

The data log does not contain this time any more, but the event log and one of the PCNS client logs shows this time frame too. The data from the 15.06.2013 were my testing with pulling out the power cord.

Best regards

Andreas

See Answer In Context

Attachments
apc.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

1. We have installed new batteries this year in February,

2. The current runtime shows me 29 minutes.

3. The shutdown is configured very simple: If the UPS goes on battery due to an input power problem the the first virtual server will start to shutdown after 540 seconds and the last one after 600 seconds. (4 virtual servers in total.) Two other physical clients will shutdown after 580 seconds. Finally the HA-host for the virtual servers begins the shutdown with the last virtual server after 600 seconds. None of the PCNS clients will turn of the UPS.

4. We had shutdown all systems and UPS on June 15th for maintenance work and to install air condition into the very small server room.

BR

Andreas

Reply

Link copied. Please paste this link to share this article on your social media post.

bernd_apc
Ensign bernd_apc
Ensign

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

Hi,

i recently had the same problem. The cause were the network switches. We had a total black out in our campus, so the switches didn't have power. Then of course the shutdown procedure couldn't run as expected. Attaching the switches to the UPS, testing, and everything went fine.

Bernd

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:04 AM

Hi Bernd,

all communication hardware is also running on the UPS, modem Switches, phone system, router... Therefore the runtime is lower than in our second plant with similar load but less other hardware.

BR Andreas

  • Tags:
  • error
  • power
  • problem
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:03 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:04 AM . Last Modified: ‎2024-03-13 12:03 AM

Recently a digger had hit a ground power wire and in our area power was off for approx one hour.

Our Smart-UPS RT 8000 RM XL had only created this event:

     UPS: The output power is turned off due to a low battery.

No signal to the PCNS clients and consequently no planned shut-down behaviour has occurred.

This week-end I have tested the whole setup manually by just simply pulling out the power cord from the UPS. The intended event communication has started and all systems were properly shut-down after the configured amount of time.

Question: Why had the ups not worked as expected? What could we do to prevent hard power off event, when the UPS does not report itself the input power failure? Have we something missed?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

0 Likes
0
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

Hi Andreas Jantz - sounds strange especially if you pulled the plug/tripped a breaker to the UPS and it worked fine.

What would be most helpful is the log files from any PCNS clients as well as the management card itself. For the management card logs, can you download them and let me know the date/time to look at? Instructions are @ the knowledge base (FAQ ) and refer to article ID FA156131. For PCNS, you'll need to access your clients and just copy and paste the log to a text file as I don't think PCNS has a log export function.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

0 Likes
0
1290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:05 AM . Last Modified: ‎2024-03-13 12:03 AM

Hi Angela,

thank you for your quick reply and help. The log files are attached. The issue has happened on

23.05.2013    14:55:49    UPS: The output power is turned off due to a low battery.    0x0114

The data log does not contain this time any more, but the event log and one of the PCNS client logs shows this time frame too. The data from the 15.06.2013 were my testing with pulling out the power cord.

Best regards

Andreas

Attachments
apc.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of