Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Smart-UPS RT 5000 battery calibration question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 battery calibration question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
6
1737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Smart-UPS RT 5000 battery calibration question

 Hello, I have a Smart-UPS RT 5000 model and I'm trying to run a battery calibration on it. The question is that during this process the load (which consists of server and other network equipment) will be shut down ?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • calibration
  • shutdown
  • smart-ups
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1737
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Hello Andrei,

There are two types of calibrations - Manual and User Commanded and depending on the method that you will use, there is a possibility of load drop.

User Commanded:

  • This is the preferred method for all Smart-UPS except for models beginning with SU (IE: SU700NET). 
  • Calibration is initiated from Power Chute Business Edition, the Network Management Card, or the LCD Screen of the UPS (if so equipped).
  • Ensure that the normal load is attached
  • Ensure Battery is charged to 100% before beginning Calibration
  • Load should be more than 30% for best results
  • UPS will drain the battery, then switch back online and charge back up
  • Calibration must not be interrupted to deliver valid results

 

Manual Calibration:
  • This is the preferred method for "SU" series Smart-UPS, or any time that a User Commanded Calibration is not possible
  • Stop the Power Chute software from running and disconnect the serial, USB, or Ethernet cable(s).
  • There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. THIS IS IMPORTANT
  • Attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power
  • Allow the unit to run on battery until it turns off completely. The load attached to the UPS will drop.
  • If the Load is not at least 30% or if the calibration is ended before the UPS drops the load, the calibration will not work.
  • Plug the UPS back into the wall outlet and allow it to recharge (preferably turned off)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1738
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Hello Andrei,

There are two types of calibrations - Manual and User Commanded and depending on the method that you will use, there is a possibility of load drop.

User Commanded:

  • This is the preferred method for all Smart-UPS except for models beginning with SU (IE: SU700NET). 
  • Calibration is initiated from Power Chute Business Edition, the Network Management Card, or the LCD Screen of the UPS (if so equipped).
  • Ensure that the normal load is attached
  • Ensure Battery is charged to 100% before beginning Calibration
  • Load should be more than 30% for best results
  • UPS will drain the battery, then switch back online and charge back up
  • Calibration must not be interrupted to deliver valid results

 

Manual Calibration:
  • This is the preferred method for "SU" series Smart-UPS, or any time that a User Commanded Calibration is not possible
  • Stop the Power Chute software from running and disconnect the serial, USB, or Ethernet cable(s).
  • There must be at least a 30% load attached to the UPS during this procedure, and this load cannot fluctuate more than +/- 5%. THIS IS IMPORTANT
  • Attach a non-critical load to the UPS and then force the UPS on battery by disconnecting it from utility power
  • Allow the unit to run on battery until it turns off completely. The load attached to the UPS will drop.
  • If the Load is not at least 30% or if the calibration is ended before the UPS drops the load, the calibration will not work.
  • Plug the UPS back into the wall outlet and allow it to recharge (preferably turned off)
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Thank you for the answer...so If I understood correctly If I initiate the calibration procedure from the web interface (method 1 ) it won't have any load drop ?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

That is correct Andrei.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1739
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Thank you for information Jonathan!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

Sir my question is not about calibration.. My question is up to how many battery packs can a Smart UPS SRT5000KXLI can support? Because i installed 2 battery packs already and on the third battery pack when I plugged the third battery pack it gives me an error of over voltage or something. Also if I update the firmware of UPS will it give the setting that i can install/mount more battery packs? Coz in the product manual i have read that it can support up to 10 battery packs.. Thank you sir..

Gerard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

0 Likes
0
1740
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 09:04 PM . Last Modified: ‎2024-03-06 11:58 PM

I have 8 battery packs running on a similar model UPS. I'm thinking if you received an overvoltage??? that to me would indicate a voltage problem in that particular battery pack, maybe something is not wired correctly, usually you have about 52 volts DC from each group o4 4 batteries, 4 * 13 = 52 volts and each deck has 2 sets of those batteries. Im thinking I would measure the voltage on that one deck. Batteries would not otherwise be overvoltage unless maybe hooked up wrong internally?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of