Smart-UPS RT 5000 XL Network spikes during SNMP monitoring

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 5000 XL Network spikes during SNMP monitoring
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
6
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

Smart-UPS RT 5000 XL Network spikes during SNMP monitoring

Hi,

We are experiencing random "high collision" events logged by our HP Procurve switches on the Smart-UPS RT 5000 XL ports while the UPS is being SNMP monitored - these take the normally idle port up to 90% utilization and are quite disruptive.
"About UPS" shows firmware version is "3" -
are there release notes for newer firmware that perhaps resolve this?

thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

these network management cards are older and yes, you have the latest firmware already.

are you using HTTPS, SSH, and is it SNMPv1 or SNMPv3? since these cards are older, they have a more difficult time supporting all of these secure connection methods at the same time and could bog it down.

yes, i would set the port speed specifically on the NMC eventually but i assume if its still set to auto, the switch will force it to 100M/full duplex anyway. might be good to see if there is a difference when you let the NMC still use auto and then force it.

i'd also be curious if these NMCs do this with a default configuration if you were able to reset one to defaults.

lastly, if using HTTPS, there was just a recent microsoft security update -> http://support.microsoft.com/kb/2661254 that blocks 768 key bit lengths. if you are using HTTPS and the NMC is using a self signed/generated certificate, it'd be 768 bits. this could prevent HTTPS access via the web UI if you were using windows and had this update applied. it was fresh in my mind so i figured i'd note it. the work around for that would be to use our security wizard tool to create a 1024 bit cert.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

I received this notice, but I don't see it in the forum - so I'll post it and reply

You are watching the thread "Smart-UPS RT 5000 XL Network spikes during SNMP monitoring", which was updated on Aug 16, 2012 9:53:05 AM by Angela:

<Referenced content removed

For your convenience, the new message is included below:
--------------------------------------------------------------
we are not aware of an issue with this. the UPS itself probably has a network management card so we need to know the model of that - AP9619 or AP9631 most likely, and the firmware of that. Can you log in via the web UI and see under Administration->General->About and tell me what you have there.

it also might be helpful to indicate what port speed these are operating on and if you are using SNMPv1 or V3 and how often the UPS is being polled via SNMP and how many values at a time.

thanks
--------------------------------------------------------------

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

Ok, here is more information

The WEB UI responds very slowly and after 3-4 clicks STOPS responding at all.
I've tried 4-5 different UPSes - same result - none of them respond on the web UI anymore, although they respond to SNMP - so I pulled the sysDescr which looks like it has firmware versions:

SNMPv2-MIB::sysDescr.0 = STRING: APC Web/SNMP Management Card (MB:v3.9.2 PF:v3.7.3 PN:apc_hw02_a
os_373.bin AF1:v3.7.2 AN1:apc_hw02_sumx_372.bin MN:AP9619 HR:A10 SN: ZA0627006748 MD:06/28/2006)
(Embedded PowerNet SNMP Agent SW v2.2 compatible)

I also noticed just hitting the web UI seems to trigger the "high collision" events on the UPS switch ports - so its not random - we can reproduce it quite easily.

Please advise which firmware we could update

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

The switch sees these UPS ports operating at 100Mb - some Half Duplex, some Full Duplex.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

So

apc_hw02_sumx_372.bin means the NMC is on v3.72
and MN:AP9619 is the model of the NMC?

I think 3.72 is the latest firmware for this network management card?

We might try hard coding the 100FullDuplex on the switch next (should we do it in ht the config.ini as well)?

After I ssh'ed into the NMC and rebooted, the Web UI was responsive again

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

we are not aware of an issue with this. the UPS itself probably has a network management card so we need to know the model of that - AP9619 or AP9631 most likely, and the firmware of that. Can you log in via the web UI and see under Administration->General->About and tell me what you have there.

it also might be helpful to indicate what port speed these are operating on and if you are using SNMPv1 or V3 and how often the UPS is being polled via SNMP and how many values at a time.

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

0 Likes
0
1260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:00 AM . Last Modified: ‎2024-03-11 03:19 AM

these network management cards are older and yes, you have the latest firmware already.

are you using HTTPS, SSH, and is it SNMPv1 or SNMPv3? since these cards are older, they have a more difficult time supporting all of these secure connection methods at the same time and could bog it down.

yes, i would set the port speed specifically on the NMC eventually but i assume if its still set to auto, the switch will force it to 100M/full duplex anyway. might be good to see if there is a difference when you let the NMC still use auto and then force it.

i'd also be curious if these NMCs do this with a default configuration if you were able to reset one to defaults.

lastly, if using HTTPS, there was just a recent microsoft security update -> http://support.microsoft.com/kb/2661254 that blocks 768 key bit lengths. if you are using HTTPS and the NMC is using a self signed/generated certificate, it'd be 768 bits. this could prevent HTTPS access via the web UI if you were using windows and had this update applied. it was fresh in my mind so i figured i'd note it. the work around for that would be to use our security wizard tool to create a 1024 bit cert.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of