Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84805members
354261posts

Smart-UPS RT 3000 XL: sTUCK IN BYPASS

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

Solved
BillP
Administrator Administrator
Administrator
0 Likes
4
363

Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This question was originally posted by Jack on APC forums on 5/24/2010


I have a UPS in MY SF office (4 months old0 that is in bypass

Warning Alarm Present
In Bypass: UPS Switch


IS there a way I can remotely put this unit online?

IF not physically? If so will the servers connected to it loose power when we switch over?

Thanks


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
363

Re: Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This reply was originally posted by Jack on APC forums on 5/25/2010


Thanks for the update However the GUI does have a option to move off by pass

See below

UPS Control

Reboot UPS
Turn UPS Off
Put UPS to Sleep
Return UPS from Bypass

Signal PowerChute® Server Shutdown

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
363

Re: Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This reply was originally posted by Jack on APC forums on 5/24/2010


Thanks for the quick response

Is there anything onthe GUI to move to bypass?

If not I'll schedule this off hrs as you mentioned we might have power interuption fro bypass to UPS?

This type of transfer doesn't cause power loss to larger UPS transfers as onthe Liebert units

BillP
Administrator Administrator
Administrator
0 Likes
0
363

Re: Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This reply was originally posted by Jack on APC forums on 5/24/2010


Excellent I found it in the GUI I'll attempt it later in the week Thanks

UPS Control

Reboot UPS
Turn UPS Off
Put UPS to Sleep
Return UPS from Bypass

BillP
Administrator Administrator
Administrator
0 Likes
0
363

Re: Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This reply was originally posted by Matt on APC forums on 5/25/2010


Unfortunately, if the UPS reports status: In Bypass: UPS Switch, the ONLY way to bring it back online is to physically set the bypass switch back to the on-line position. The UPS will not accept a command via software or Network Mangagement Card to override the actual switch.

Coming back online will not interrupt the UPS output to your attached equipment. The transition online will occur within 2 seconds of disabling the bypass switch on the rear of the UPS.

BillP
Administrator Administrator
Administrator
0 Likes
0
364

Re: Smart-UPS RT 3000 XL: sTUCK IN BYPASS

This reply was originally posted by Jack on APC forums on 5/25/2010


Thanks for the update However the GUI does have a option to move off by pass

See below

UPS Control

Reboot UPS
Turn UPS Off
Put UPS to Sleep
Return UPS from Bypass

Signal PowerChute® Server Shutdown