Smart-UPS RT 2200 XL with new batteries and no self-test or runtime calibration

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 2200 XL with new batteries and no self-test or runtime calibration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
1
690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

Smart-UPS RT 2200 XL with new batteries and no self-test or runtime calibration

The UPS has 3.5 years. Last week there was a power outage for a few minutes and the UPS acted as if there were no batteries: the computers were turned off ...

Before the power came back I did some testing. The only things I could do: push the button to turn off and all LEDs turned off. After I pressed the power button, releasing the second beep and there was a sequence of LED lighting and deleting and relays noises, ending with the Fault LED on.

At my command it starts the self-test or calibration, but soon abandons any of the two.

As the batteries may have been old, I decided to change them. The same thing happens. I tried to calibrate with more than 30% load and the reactions are always the same: Relay noises, LEDs in a sequence, ending with the fault LED on.

I put below state data and event log:

Last Diagnostic Results

              

Self-test Result                 No Result Available

Self-test Date                   Janeiro 2015

Runtime Calibration Result                         Cancelled

Runtime Calibration Date                            Janeiro 2015

Bypass Status

              

Current Status                  Not In Bypass

              

UPS System Parameters Status

              

Device Status                    On line

UPS Load                           0,0 %

Runtime Remaining                        150 Minutes

Internal Temperature                    29,6 °C / 85,3 °F

Load Power                       0 % VA

Load Current                     0 A

 

Power Status

Line Voltage                      120,9 VAC

Output Voltage                120,2 VAC

Output Frequency                           60,0 Hz

 

Battery Status

Battery Charge                 100,0 %

Battery Voltage                54,3 VDC

Total Battery Packs                        1

 

 

27/01/15             09:43:32              Bypass Ended

27/01/15             09:43:24              Self Test Initiated

27/01/15             09:43:20              UPS In Bypass Due To Internal Fault

27/01/15             09:43:20              Calibration Cancelled

27/01/15             09:43:16              Calibration Started

27/01/15             09:28:34              Bypass Ended

27/01/15             09:28:26              Self Test Initiated

27/01/15             09:28:22              UPS In Bypass Due To Internal Fault

27/01/15             09:28:22              Calibration Cancelled

27/01/15             09:28:17              Calibration Started

26/01/15             19:19:07              Bypass Ended

26/01/15             19:18:55              UPS In Bypass Due To Internal Fault

26/01/15             19:18:55              Self Test Initiated

Thanks in advance.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • calibration
  • fail
  • led
  • runtime
  • self-test
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
690
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

It sounds like your UPS was likely in bypass operation when you had the power outage. It appears to be in bypass (operating on utility power) because of an internal fault. Based on what you describe and what I see in the log, I think your UPS likely requires some repair (or replacement) depending on where you're located and its warranty status. cry

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

0 Likes
0
691
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM

It sounds like your UPS was likely in bypass operation when you had the power outage. It appears to be in bypass (operating on utility power) because of an internal fault. Based on what you describe and what I see in the log, I think your UPS likely requires some repair (or replacement) depending on where you're located and its warranty status. cry

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of