Smart-UPS RT 2200 XL with new batteries and no self-test or runtime calibration
  • Smart-UPS RT 2200 XL with new batteries and no self-test or runtime calibration
145
Posted: ‎2021-06-27 11:32 PM . Last Modified: ‎2024-03-19 12:05 AM
1016
The UPS has 3.5 years. Last week there was a power outage for a few minutes and the UPS acted as if there were no batteries: the computers were turned off ...
Before the power came back I did some testing. The only things I could do: push the button to turn off and all LEDs turned off. After I pressed the power button, releasing the second beep and there was a sequence of LED lighting and deleting and relays noises, ending with the Fault LED on.
At my command it starts the self-test or calibration, but soon abandons any of the two.
As the batteries may have been old, I decided to change them. The same thing happens. I tried to calibrate with more than 30% load and the reactions are always the same: Relay noises, LEDs in a sequence, ending with the fault LED on.
I put below state data and event log:
Last Diagnostic Results
Self-test Result                 No Result Available
Self-test Date                   Janeiro 2015
Runtime Calibration Result                         Cancelled
Runtime Calibration Date                            Janeiro 2015
Bypass Status
Current Status                  Not In Bypass
UPS System Parameters Status
Device Status                    On line
UPS Load                           0,0 %
Runtime Remaining                        150 Minutes
Internal Temperature                    29,6 °C / 85,3 °F
Load Power                       0 % VA
Load Current                     0 A
Power Status
Line Voltage                      120,9 VAC
Output Voltage                120,2 VAC
Output Frequency                           60,0 Hz
Battery Status
Battery Charge                 100,0 %
Battery Voltage                54,3 VDC
Total Battery Packs                        1
27/01/15             09:43:32              Bypass Ended
27/01/15             09:43:24              Self Test Initiated
27/01/15             09:43:20              UPS In Bypass Due To Internal Fault
27/01/15             09:43:20              Calibration Cancelled
27/01/15             09:43:16              Calibration Started
27/01/15             09:28:34              Bypass Ended
27/01/15             09:28:26              Self Test Initiated
27/01/15             09:28:22              UPS In Bypass Due To Internal Fault
27/01/15             09:28:22              Calibration Cancelled
27/01/15             09:28:17              Calibration Started
26/01/15             19:19:07              Bypass Ended
26/01/15             19:18:55              UPS In Bypass Due To Internal Fault
26/01/15             19:18:55              Self Test Initiated
Thanks in advance.
  • calibration
  • fail
  • led
  • runtime
  • self-test
It sounds like your UPS was likely in bypass operation when you had the power outage. It appears to be in bypass (operating on utility power) because of an internal fault. Based on what you describe and what I see in the log, I think your UPS likely requires some repair (or replacement) depending on where you're located and its warranty status. cry