Smart-UPS RT 15000 XL Error:"The battery power is too low to support the load" AFTER SelftTest

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 15000 XL Error:"The battery power is too low to support the load" AFTER SelftTest
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
122
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
9
2541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

Smart-UPS RT 15000 XL Error:"The battery power is too low to support the load" AFTER SelftTest

After the first Self test, the UPS sends email alerts every 2 minutes:

Critical Alarm 1 Critical Alarm Present 

  • The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

I've already restarted a management card but the error is still shown via web interface(network management card).

But the "fault" LED is OFF on the APC Smart-UPS.

Any thoughts ?

p.s.

I opened a support case 3 days ago.. but APC support seems to be very very slow 😞 may be somebody in community can help me, before I get an answer from apc support.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

Ok, so I still need to know your available runtime on the UPS? I bet it is 22 minutes or less. Can you confirm? According to the data log, you also have between a 40-50% load across your three phases.

I ask because I see that in your config.ini, you have LowBatteryDuration=20 which indicates someone has changed the "low battery duration" or the amount of runtime when the UPS declares it has a low battery to 20 minutes. The UPS is trying to tell you if you have a power outage, it is going to immediately declare a "low battery" and force everything to shutdown (like PowerChute clients) while it runs for the 20 minute duration. The default for this setting is 2 minutes so someone changed it and we need to find out why or understand so we can determine if it was in error or not. But, it is causing the alarm.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2541
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

Hello

It is likely that perhaps the UPS batteries are failing or that you have changed a setting that causes this. I can explain more when you provide the log files from the UPS Network Management Card. If anything, this message comes from the UPS, not the management card - the management card is just telling you what the UPS reported.

A few questions:

  • Please provide log files - config.ini, event.txt, data.txt - instructions here -> How can I download Event, Data, Configuration, and Debug files from my Network Management Card? | FA...
  • What is the total reported UPS runtime in the Network Management Card?
  • How old are the batteries/UPS? (the fix six characters of the UPS serial number can help confirm this)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

The ups was bought in Dec.2013. The ups and the batteries are new.

Runtime Remaining: 21min.

I've generated a Debug/Logs file. where can I upload it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:34 AM . Last Modified: ‎2024-03-12 03:38 AM

config.ini

data.txt

event.txt


Attachments
event.txt.zip
data.txt.zip
config.ini.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

I don't really need the debug logs but I'll take it. You can click "use advanced editor" on your reply window here on the community and it will allow you to upload attachments.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2542
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

Ok, so I still need to know your available runtime on the UPS? I bet it is 22 minutes or less. Can you confirm? According to the data log, you also have between a 40-50% load across your three phases.

I ask because I see that in your config.ini, you have LowBatteryDuration=20 which indicates someone has changed the "low battery duration" or the amount of runtime when the UPS declares it has a low battery to 20 minutes. The UPS is trying to tell you if you have a power outage, it is going to immediately declare a "low battery" and force everything to shutdown (like PowerChute clients) while it runs for the 20 minute duration. The default for this setting is 2 minutes so someone changed it and we need to find out why or understand so we can determine if it was in error or not. But, it is causing the alarm.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

You was right!

I changed the LowBatteryDuration to 2 min. and it solved the issue! I don't have any Errors any more!

I really appreciate your help!

The available runtime on this UPS = 21min.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

I changed it, I wanted the UPS not to shutdown itself for 20minutes, if I get a power outage.

I think I missunderstood this Settings.. what does it mean exactly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

Do you know why you changed it though? It could affect something else.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

0 Likes
0
2543
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:35 AM . Last Modified: ‎2024-03-12 03:38 AM

The setting defines when the UPS declares a low battery to attached devices running PowerChute software. So, the UPS will always run the entire time (about 20 minutes in your case) and then turn off. The only time it may shut down earlier is if you were using PowerChute Network Shutdown clients and they received the signal from the UPS Management Card at the 20 minute mark. The UPS will continue to run and PowerChute will begin its shutdown progress and shut down your server or whatever is running PowerChute. The user has the option in PowerChute to tell the UPS to turn off after it is done shutting down and if your server only takes 3 minutes to shutdown, it could potentially shutdown earlier than the 20 minutes.

Basically, if you don't use PowerChute, you can leave it at 2 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of