Smart-UPS RT 15000 RM XL error msgs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 15000 RM XL error msgs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
1
1418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

Smart-UPS RT 15000 RM XL error msgs

Our power went out due to storms.  Generator kicked in.  I've received 142 msgs fromr 6:30 pm - 12 pm.  Electric is still out and power generator did kick in. NOt sure what to do or if this is going to cause more problems with my equipment.  These are the msgs that we keep receiving over and over. 

 04/09/2015 23:47:52 Device UPS: A phase synchronization fault no longer exists.
 04/09/2015 23:47:52 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode.
 04/09/2015 23:47:31 Device UPS: A phase synchronization fault exists.
 04/09/2015 23:47:28 Device UPS: An input voltage or frequency problem prevents switching to bypass mode.
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
0
1419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

Hi Carol,

I hope you're doing OK in the storms, they made the national news!

I believe you don't need to worry about these messages under these conditions. The UPS should be performing it's intended function without a problem! The more significant one is "... prevents switching to bypass mode". You said "power generator did kick in", so I assume you mean the generator is powering the UPS now. These messages are trying to tell you the UPS is not altogether happy with the generator power, and if the UPS had an internal fault, or became overloaded, it would shutdown the output, thus dropping any connected loads, rather than passing "raw" generator power to the load with the potential to damage the connected equipment caused by the perceived "bad" generator power. It is possible that some of the UPS / Configuration / Power settings accessible through the NMC could reduce or eliminate these messages by widening the range of voltage or frequency the UPS will accept from the generator. I'm not familiar with the precise meaning of "phase sychronization fault", or any other settings you may be able to access, but since it seems to come and go, I would guess it's related to a speed regulation issue with the generator. Also, I'm running an older generation Network card (AP9619), so if you have the current gen NMC, you may have different settings than I have mentioned.

In short-- if these are the only message you're getting-- relax, the UPS should be fine!

Wayne

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
0
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

Hi Carol,

I hope you're doing OK in the storms, they made the national news!

I believe you don't need to worry about these messages under these conditions. The UPS should be performing it's intended function without a problem! The more significant one is "... prevents switching to bypass mode". You said "power generator did kick in", so I assume you mean the generator is powering the UPS now. These messages are trying to tell you the UPS is not altogether happy with the generator power, and if the UPS had an internal fault, or became overloaded, it would shutdown the output, thus dropping any connected loads, rather than passing "raw" generator power to the load with the potential to damage the connected equipment caused by the perceived "bad" generator power. It is possible that some of the UPS / Configuration / Power settings accessible through the NMC could reduce or eliminate these messages by widening the range of voltage or frequency the UPS will accept from the generator. I'm not familiar with the precise meaning of "phase sychronization fault", or any other settings you may be able to access, but since it seems to come and go, I would guess it's related to a speed regulation issue with the generator. Also, I'm running an older generation Network card (AP9619), so if you have the current gen NMC, you may have different settings than I have mentioned.

In short-- if these are the only message you're getting-- relax, the UPS should be fine!

Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore