SURT192XLBP with SURT6000XLT

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURT192XLBP with SURT6000XLT
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

0 Likes
3
1087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

SURT192XLBP with SURT6000XLT

Hello, I have purchased empty SURT192XLBP, and I have one SURT6000XLT. My question is, what volatge should I have to measure in the battery connectors in the SURT192XLB.?

Just to be sure about the DC voltage before I connect them to the UPS battery connectors in the rear panel.

BR, José

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • surt192xlbp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

Hi again José,

Oh ok.

Yes, you're correct - for SURT6000XLT, (16) 12v modules wired together in series to give you 192vDC is what is in this model UPS and battery pack. There are two strings in each - 8 modules a piece. The part number for the batteries is APCRBC140 (which just replaced RBC44 which will also work) which comes with these two strings. (Some of the larger SURT models use (4) strings, or (2) APCRBC140 and the voltage on the bus is the same so the additional (2) strings are wired in parallel to give additional runtime but the voltage remains the same).

You can connect up to (10) SURT192XLBP external battery packs to this UPS.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

Hi Jose,

This UPS and battery pack have a nominal 192vDC voltage battery bus which should float at ~210-218vDC. The SURT192XLBP needs to have batteries installed though for it to read any voltage so I was a little confused when you said it is empty.

In general, it is a bad idea to mix new and old batteries as the older batteries can damage the newer ones. I just wanted to mention it relating to this situation.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

Thanks for the reply.

The SURT6000XLT has the internal batteries brand new, the UPS is a brand new one.

So I have purchased one SURT192XLBP without internal batteries, so I have purchased new batteries and will install them in the SURT192XLBP.

I am just double checking.

So they are 16 batteries in series that will measure nominal 192VDC at each "white" battery connector, right.?

And, how many SURT192XLBP, can I add to my SURT6000XLT.?

BR, José

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

0 Likes
0
1087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:50 PM

Hi again José,

Oh ok.

Yes, you're correct - for SURT6000XLT, (16) 12v modules wired together in series to give you 192vDC is what is in this model UPS and battery pack. There are two strings in each - 8 modules a piece. The part number for the batteries is APCRBC140 (which just replaced RBC44 which will also work) which comes with these two strings. (Some of the larger SURT models use (4) strings, or (2) APCRBC140 and the voltage on the bus is the same so the additional (2) strings are wired in parallel to give additional runtime but the voltage remains the same).

You can connect up to (10) SURT192XLBP external battery packs to this UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore