Smart-UPS RT 1500 XL site wiring faults
  • Smart-UPS RT 1500 XL site wiring faults
5060
140
Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM
983
I have a a Smart-UPS RT 1500 XL which is sending out traps/messages flapping between a site wiring fault exists, and condition has cleared.  The doc says to have a qualified electrician inspect (for site wiring fault), but with it continuously flapping back and forth between ok/not ok, is there anything else I should be looking for?
Yes it is.  I was looking for other ideas since it is flapping so much, and I'm remote to the UPS, so I can't see for myself what is plugged in. I'll find out what else is plugged into the UPS.
Hi Chris,
Is this what you reviewed? http://www.apc.com/us/en/faqs/FA158817
The other possible causes for a site wiring fault would be:
1. Overloaded neutral wire (>5 VAC measured between Neutral and Ground).
2. Reversed polarity (hot and neutral wires are reversed).
3. Missing or loose ground wire. (Note: this also includes using a 3 prong to 2 prong adapter)
I would look at what else is on the same circuit as your UPS, including anything connected to the UPS. One of those other pieces of equipment could be causing a problem with an overloaded neutral maybe or some other issue. I would assume the issue is not reversed polarity since you said it is coming and going. That leaves item #1 or #3 most likely.