Smart-UPS RT 1500 XL site wiring faults
I have a a Smart-UPS RT 1500 XL which is sending out traps/messages flapping between a site wiring fault exists, and condition has cleared. The doc says to have a qualified electrician inspect (for site wiring fault), but with it continuously flapping back and forth between ok/not ok, is there anything else I should be looking for?
Thanks
- Labels:
-
Smart-UPS & Symmetra LX | RM
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 06:21 AM . Last Modified: 2024-03-18 02:27 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:21 AM . Last Modified: 2024-03-18 02:27 AM
Yes it is. I was looking for other ideas since it is flapping so much, and I'm remote to the UPS, so I can't see for myself what is plugged in. I'll find out what else is plugged into the UPS.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:21 AM . Last Modified: 2024-03-18 02:27 AM
Hi Chris,
Is this what you reviewed? http://www.apc.com/us/en/faqs/FA158817
The other possible causes for a site wiring fault would be:
1. Overloaded neutral wire (>5 VAC measured between Neutral and Ground).
2. Reversed polarity (hot and neutral wires are reversed).
3. Missing or loose ground wire. (Note: this also includes using a 3 prong to 2 prong adapter)
I would look at what else is on the same circuit as your UPS, including anything connected to the UPS. One of those other pieces of equipment could be causing a problem with an overloaded neutral maybe or some other issue. I would assume the issue is not reversed polarity since you said it is coming and going. That leaves item #1 or #3 most likely.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 06:21 AM . Last Modified: 2024-03-18 02:27 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:21 AM . Last Modified: 2024-03-18 02:27 AM
Yes it is. I was looking for other ideas since it is flapping so much, and I'm remote to the UPS, so I can't see for myself what is plugged in. I'll find out what else is plugged into the UPS.