device behind APC AP7723 ATS reloads while preferred source is available

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • device behind APC AP7723 ATS reloads while preferred source is available
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
4
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

device behind APC AP7723 ATS reloads while preferred source is available

I have a Cisco switch, which is connected to AP7723(firmware 2.0.1) ATS. AP7723 has two source feeds- preferred "source A" is connected to mains power and "source B" is connected to UPS. UPS is not manageable. The problem is, that in some occasions ATS redundancy is lost because something happens with the UPS. This is a remote site and as I told, I'm not able to manage UPS remotely. The problem is, that at the very same time when "source B" is lost, the switch reloads for some reason. This shouldn't happen because ATS doesn't even use "source B":

---
ATS Status
Source A selected, Switchover Possible

Selected Source : Source A
Preferred Source : Source A
---

ATS itself has never reloaded. It's only the switch behind the ATS which reloads at the very same time when something happens with the "source B".

What might cause such issue? Aren't there filters in AP7723 which assure that disturbance introduced on the sources are filtered out for outlets? All suggestions/thoughts are most welcome πŸ™‚

Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
  • Tags:
  • christian
  • louboutin
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
0
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

sorry - missed this post.

can you post the other files i asked for too? i'd like to see the full data and event logs if possible. furthermore, we made significant changes dealing with ATS behavior in the newer firmware. i would definitely think about upgrading and seeing if the same behavior exists. [information here on the upgrade process|http://nam-en.apc.com/app/answers/detail/a_id/11107].

lastly, please be advised that the ATS has a break before make transfer type. this includes a transfer time of 8-12ms, with 16-18ms maximum. the power supply in the cisco switch might not be able to handle that but i am not sure that is the case before i see the full logs. [see technical reference here|http://www.apcmedia.com/salestools/THON-7GTPY6_R5_EN.pdf]

you also didnt mention if this is the only piece of load the reboots and other stuff doesnt. or is this the only thing attached to the ATS?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
0
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

can you provide the full event, data, and config.ini files? (instructions are here for that.) also, can you point out in this log when you've seen the Cisco switch reboot? is there any other equipment attached to the ATS? if so, does that reboot?

also, i might consider upgrading your ATS if possible for other benefits and fixes. i am not saying it will fix the issue here since i don't know what it is yet, but i noticed you indicated you have firmware 2.0.1 on the ATS itself. we have an upgrade which will update the ATS network management card and the ATS to 2.0.3.

take a look here if interested -> http://nam-en.apc.com/app/answers/detail/a_id/11107/

the file would be available from here -> http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7723&tab=software

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
0
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

i picKed a winna wrote:
can you provide the full event, data, and config.ini files? (instructions are here for that.) also, can you point out in this log when you've seen the Cisco switch reboot? is there any other equipment attached to the ATS? if so, does that reboot?
also, i might consider upgrading your ATS if possible for other benefits and fixes. i am not saying it will fix the issue here since i don't know what it is yet, but i noticed you indicated you have firmware 2.0.1 on the ATS itself. we have an upgrade which will update the ATS network management card and the ATS to 2.0.3.
take a look here if interested -> [http://nam-en.apc.com/app/answers/detail/a_id/11107/]
the file would be available from here -> [http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7723&tab=software]
Content of config.ini can be found here: [http://perl.nopaste.dk/p4595]

I guess the most interesting part of the configuration file is the "ATS" section, which has following lines:

SourceAName=Feed 1
SourceBName=Feed 2
PreferredSource=SourceA
FrontPanel=Unlocked
VoltXferRange=Medium
Sensitivity=High
FrequencyDeviation=2
LineVRMS=230 Vrms
WideVRMSLimit=30 Volts
MediumVRMSLimit=23 Volts
NarrowVRMSLimit=16 Volts



In case the "Source B" is lost, I see following lines in the ATS log:

+01/16/2012 01:11:48 Automatic Transfer Switch: Fault cleared on Source B.+
+01/16/2012 01:11:47 Automatic Transfer Switch: Fault exists on Source B.+
+01/16/2012 01:11:45 Automatic Transfer Switch: Redundancy has been restored. Source B is available.+
+01/16/2012 01:11:13 Automatic Transfer Switch: ATS has lost redundancy. Source B is not available.+

..and at the same time Cisco switch connected to ATS power-cycles. There are two other switches connected to this ATS as well, but while one of those three has never power-cycled, the second one has reloaded once. All this happens always exactly the moment when "Source B" is lost.

Has anyone experienced something similar? Or what might cause this?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
0
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

What might cause behaviour described in my first post? Aren't there filters in AP7723 which assure that disturbance introduced on the sources are filtered out for outlets? All suggestions/thoughts are most welcome 😐

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

0 Likes
0
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 06:21 AM . Last Modified: β€Ž2024-03-18 02:27 AM

sorry - missed this post.

can you post the other files i asked for too? i'd like to see the full data and event logs if possible. furthermore, we made significant changes dealing with ATS behavior in the newer firmware. i would definitely think about upgrading and seeing if the same behavior exists. [information here on the upgrade process|http://nam-en.apc.com/app/answers/detail/a_id/11107].

lastly, please be advised that the ATS has a break before make transfer type. this includes a transfer time of 8-12ms, with 16-18ms maximum. the power supply in the cisco switch might not be able to handle that but i am not sure that is the case before i see the full logs. [see technical reference here|http://www.apcmedia.com/salestools/THON-7GTPY6_R5_EN.pdf]

you also didnt mention if this is the only piece of load the reboots and other stuff doesnt. or is this the only thing attached to the ATS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore