SNMP for a Fujitsu branded Smart-UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SNMP for a Fujitsu branded Smart-UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
138
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:28 AM

0 Likes
5
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:28 AM

SNMP for a Fujitsu branded Smart-UPS

Hello,

I am in the process of setting up SNMP monitoring of a UPS.

The UPS model is a Smart-UPS 750, the UPS SKU is FJT750I.

Does this support SNMP monitoring?

Thanks,

Liam

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Hi Liam,

Yes, this is making sense except for the fact you said Solar Winds is able to monitor SNMP over USB for your APC branded UPS. This is not something we offer (or that I think is even possible). I am thinking maybe you also happen to have a UPS Network Management Card installed in the APC branded UPS that is really doing the SNMP? And the USB cable happens to also be connected. If so, that same solution would work in the FJT UPS as it should also have a SmartSlot for the APC accessories?

Is it possible to check if the APC branded UPS also has an APC NMC installed to be sure?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Yes, it should if you buy a UPS Network Management Card (NMC) for it or if it came with one pre-installed. (From what I can tell online, it does not typically ship with an NMC if you specifically bought the SKU "FJT750I."

The UPS itself by default only supports monitoring over USB and serial communications. Networking monitoring like with SNMP is provided with an NMC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Thanks for your reply.

We are running a solarwinds monitoring agent on the server that the UPS USB cable is attached to, so I presume the monitoring agent would be able to capture snmp checks that way.

On another server we have the same setup, and the monitoring agent can perform snmp checks for the USB attached UPS, the difference being the UPS is an actual APC branded UPS with a model number of SMT750I.

So the difference being the one that does not work is a fujitsu branded smart-ups, the one that does is an APC branded UPS.

Would the OID/MIB be different for the Fujitsu?  If so would you know where I can get the OID/MIB information?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Hi Liam,

As far as I know, this type of stuff is not different on the FJT UPS but I am not 100% certain. But, I am still not clear how you'd be getting SNMP data over the USB cable. Via USB, there is data available that I refer to as standard UPS USB usages which would make sense to me.

Is it possible that you are looking at SNMP OIDs over the network (with NMC installed) and have USB connected?

Can you elaborate more so I can fully understand what interface we are referring to on the UPS for sure so then I could check further into it?

I was reading a bit on Solar Winds and I see Universal Device Poller as something to configure. But to me, it looks like all OID, MIB, SNMP related over the network.

My understanding at this point too is that FJT UPS would support the same SNMP MIB and OIDs as the SMT UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Hello Angela,

Yes I am looking for the SNMP OIDs over the network.

The interface on the UPS I am using is the USB interface.  The USB interface is connected to a server that has the solarwinds remote monitoring agent installed to monitor SNMP.  The agent then reports back to a central console that is cloud based.

Does this make sense?

Thanks,

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

0 Likes
0
1031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:21 AM . Last Modified: ‎2024-03-18 02:27 AM

Hi Liam,

Yes, this is making sense except for the fact you said Solar Winds is able to monitor SNMP over USB for your APC branded UPS. This is not something we offer (or that I think is even possible). I am thinking maybe you also happen to have a UPS Network Management Card installed in the APC branded UPS that is really doing the SNMP? And the USB cable happens to also be connected. If so, that same solution would work in the FJT UPS as it should also have a SmartSlot for the APC accessories?

Is it possible to check if the APC branded UPS also has an APC NMC installed to be sure?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore