Smart-UPS RT 10000 XL with NMC2 - config question about shutdown option

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 10000 XL with NMC2 - config question about shutdown option
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

0 Likes
8
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

Smart-UPS RT 10000 XL with NMC2 - config question about shutdown option

Hi,

we are using a Smart-UPS RT 10000 XL with a NMC2 (Firmware Revision: 476.18.W).

I "adopted" the UPS from my colleague and now I´m wondering about the current configuration.

jptgvLL8jHDgWu%2B6k9KmRw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpegjptgvLL8jHDgWu%2B6k9KmRw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg

Does this config make sense in out specific constellation? All the servers in our server-room do have the powerchute network shutdown client installed on, which is configured to shutdown the servers after a given period of "UPS on battery" (about 600 sec.).

Thx for your help!

Kind regards

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

Hi,

I recommend you un-check controlled early shutdown and configure using PowerChute for the individual servers. 

Setting the minimum battery capacity to 10% will cause the UPS not to turn back on until the battery has 10% charge available. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

On 6/18/2018 2:30 AM, horst said:

I`m generally wondering what kind of sense the option "UPS percent load is less than" makes for the UPS shutdown?! Why do I want the UPS to shut down in correlation to the load when it`s on battery?

So Bill talked about how you can have PowerChute shut down the UPS in which case you don't need "Controlled Early Shutdown."

How would it be used? Suppose the load on the UPS with all the servers off (just network switches and the like) is 10%. You could set it up to shut down the UPS when load is less than 12% so it automatically shuts down the UPS when the power fails and all the servers are off.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

Hi,

Assuming the runtime is sufficient than yes the configuration is fine. PowerChute will tell the computes to shutdown after being on battery for 10 minutes. The OS will begin powering down and after 7 minutes the UPS will power down.

See page 36 of the PowerChute User's Guide http://www.apc.com/salestools/PMAR-9E5LVY/PMAR-9E5LVY_R4_EN.pdf

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:40 AM

Two things that stick out to me are:
- Controlled early shutdown will start a shutdown immediately on power failure (unless your UPS is >=95% loaded... in which case you probably don't have much runtime anyways)

- Minimum battery capacity is 0%... I'd let the battery charge up a bit before turning back on in case you need to safely shut down again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

Thx for your reply!

@bill From where do you get the information that the UPS will shut down after 7 minutes?!

@voidstar for my general understanding, what "shutdown" do I configure in the UPS webinterface under "configuration" --> "shutdown" ?!

do I configure the shutdown of the clients or of the UPS?

for my comprehension the client shutdown is configured by the powerchute client, installed on the clients itself on not in the UPS.

I`m generally wondering what kind of sense the option "UPS percent load is less than" makes for the UPS shutdown?! Why do I want the UPS to shut down in correlation to the load when it`s on battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

Hi,

The information is listed in the PowerChute User's Guide on stating on page 36. The low battery and the maximum required delays are both 5 minutes so the UPS will what 5 minutes plus the additional 2 minutes and then power down. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1195
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

ok thx, I think now I get it!

do I have to configure the "controlled early shutdown" option for a proper functionality or am I able to uncheck the box at "UPS percent load is less than"?!

I´d like to set the "low battery duration" to 5 minutes and the "shutdown delay" to 120 sec.

I also would set the "minimum battery capacity" to 10%

The rest about the client shutdowns will be configured in each powerchute client, installed on the server.

I think then I should be on the save side in case of a power loss

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:44 AM . Last Modified: ‎2024-03-11 03:39 AM

Hi,

I recommend you un-check controlled early shutdown and configure using PowerChute for the individual servers. 

Setting the minimum battery capacity to 10% will cause the UPS not to turn back on until the battery has 10% charge available. 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1196
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

On 6/18/2018 2:30 AM, horst said:

I`m generally wondering what kind of sense the option "UPS percent load is less than" makes for the UPS shutdown?! Why do I want the UPS to shut down in correlation to the load when it`s on battery?

So Bill talked about how you can have PowerChute shut down the UPS in which case you don't need "Controlled Early Shutdown."

How would it be used? Suppose the load on the UPS with all the servers off (just network switches and the like) is 10%. You could set it up to shut down the UPS when load is less than 12% so it automatically shuts down the UPS when the power fails and all the servers are off.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

0 Likes
0
1194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:45 AM . Last Modified: ‎2024-03-11 03:39 AM

thx for all your replies!

since I don't know the load of the UPS when all the Servers are shut down and only the network components are left running, I unchecked the "UPS percent load less than" box and set the "UPS runtime remaining less than" box and set it to 2 minutes.

I also set the "minimum battery capacity" to 15%.

I think now the UPS should act as far as possible in a suitable way when the power gets off.

again many thx for your replies! they helped a lot!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of