Smart-UPS RT 10000 XL is going to in Bypass mode

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 10000 XL is going to in Bypass mode
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
117
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:20 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
3
2217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:20 AM . Last Modified: ‎2024-03-13 02:56 AM

Smart-UPS RT 10000 XL is going to in Bypass mode

I have received below message in Smart-UPS RT 10000 XL

UPS: Refused a self-test; UPS is overloaded.
UPS: An inverter fault exists.
UPS: In bypass in response to an internal hardware fault.

And my UPS is goes on Bypass mode. what is the problem ?
I had put two UPS out of one showing above message. And 2nd running fine. Both are given in same server IBM.
As per vendor it is problem in Battery bank or My server side. So I inter changed battery bank of both UPS but UPS 1 is goes bypass mode.

What is the solution of it kindly give reply.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
2216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

on issue #1, it probably needs to be replaced. you probably want to contact your local tech support for warranty options.

on issue #2, can you get the config.ini, event.txt, and data.txt files from this NMC using these instructions? http://nam-en.apc.com/app/answers/detail/a_id/9321/

thanks. once i see the files for #2, then we see if there is an issue. also, please point out anything in the log such as a shutdown example of when the UPS didnt power up afterwards so i know where to look.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:20 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
2216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:20 AM . Last Modified: ‎2024-03-13 02:56 AM

Hi,
We have the same problem, after installing about 14 (SUART 5000 XLI) and 10 (SUART 10000 XLI) with the default SNMP management software AP9619
1/one of 10KVA UPS faults with two errors "inverter fault+ output power turned off "impossible to bypass it too, it's the second UPS replacement of the first who works for two months normally then we should stopped it after a noisy cracksmen’s and no way to powering on it (we use it in 3~/3~ mode input/output!)
We join the Mgmt card results.
2/ the second problem for some 5KVA/UPS they working fine but after a low battery shutdown, the UPS don't restart automatically when the INPUT voltage comes back (no electrical generators exists on this sites! for instances!)

Can we have your technical ideas and experiences?
Thanks

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
2216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

The Ups Says An Inverter Fault Exist, The Inverter Must Be Repaired Or Replaced

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
2217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

on issue #1, it probably needs to be replaced. you probably want to contact your local tech support for warranty options.

on issue #2, can you get the config.ini, event.txt, and data.txt files from this NMC using these instructions? http://nam-en.apc.com/app/answers/detail/a_id/9321/

thanks. once i see the files for #2, then we see if there is an issue. also, please point out anything in the log such as a shutdown example of when the UPS didnt power up afterwards so i know where to look.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of