SURTD3000XLI not working

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SURTD3000XLI not working
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
4
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

SURTD3000XLI not working

I recently purchased a used SURTD3000XLI and tried commisioning the unit today. Powered it up and it started clicking rapidly. No lights are visable on the front panel and this with no load applied to the ups. It also tripped my earth leakage breaker at the mains board. I had to pull the one battery lead out to stop the clicking relay. Please advise. the unit is still under warranty till March 2012.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

Hi Warren,

Let us start by making sure that the internal batteries are properly connected. Then make sure that the required voltage is provided with the correct wiring. When did it tripped the breaker? Did it tripped the moment you plug the UPS or when you turned it on? See if this would help, while the UPS is off and unplugged press and hold the I/Test button. While holding the button you'll hear a short and a long beep. As soon as you hear the long beep, release the button. This should power up the UPS on battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

Did anyone ever find a solution to this? I have the same model, showing the same symptoms on startup. The batteries are at 208v at rest but when test button is pushed, the voltage drops to 70v, the fan spins intermittently as a relay clicks on and off.

When AC is applied the same thing happens ( battery voltage drops ), and the circuit breaker at the switchboard trips.

The batteries recover within seconds to 208v. when either the test button is released or AC is disconnected. Any ideas?

Colin.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

I understand from either knowledge base article FA156604 and previous posts to the forum that at least 85 volts per battery module (170 across the pair) in an Smart-UPS RT (those which use RBC44) is required in order for it to start up. Anything less and it will exhibit the clicking and "flapping" behavior you are likely seeing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

Thanks for that Battman.

As mentioned, the batteries have 208v across the pair until the test button is pressed or AC is applied, when it drops to 70v ( across the pair ) . I am trying to find out if this is likely to be a battery problem or a hardware fault.

Regards, Colin

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

0 Likes
0
815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:21 AM . Last Modified: ‎2024-03-13 02:56 AM

Hi Warren,

Let us start by making sure that the internal batteries are properly connected. Then make sure that the required voltage is provided with the correct wiring. When did it tripped the breaker? Did it tripped the moment you plug the UPS or when you turned it on? See if this would help, while the UPS is off and unplugged press and hold the I/Test button. While holding the button you'll hear a short and a long beep. As soon as you hear the long beep, release the button. This should power up the UPS on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of