Can the curcuit break switch themselves off from an overload or anything?
We had a power outage and we have a couple APC ATS AP7721 transfer switches but for some reason the power from one UPS was off.. logs on the ATS shows redundency was lost at the time of the outage.
I cant find any logs to say there was an issue on the UPS apart from the power failure itself.
regards,
Adrian
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:35 AM . Last Modified: 2024-03-19 01:25 AM
The output breakers on the RT units can be tripped by an overload. The point at which they will do so will depend on the model/breaker size. You can attach the data/event logs from both the ATS and the UPS here as attachments if you wish.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 04:35 AM . Last Modified: 2024-03-19 01:25 AM
The output breakers on the RT units can be tripped by an overload. The point at which they will do so will depend on the model/breaker size. You can attach the data/event logs from both the ATS and the UPS here as attachments if you wish.