SYMMETRA UPS E3 ALARM MESSAGE

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMMETRA UPS E3 ALARM MESSAGE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

0 Likes
1
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

SYMMETRA UPS E3 ALARM MESSAGE

Can you please advise what is the meaning of the alarm message E3 on Symmetra UPS. Morever, the UPS did not go to battery back up when the power failed, The battery banks are OK.

Innovator

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Tags:
  • alarm
  • e3
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

From a public APC Knowledge Base:

The "E3" error message on the Symmetra XR Frame is an indication of lost communication between the Symmetra Power Array and the Symmetra Extended Run Battery Frame. This error message will cause a fault LED on the PowerView on the Symmetra Power Array and will result in the loss of communication between the two frames where the Power Array will not be able to recognize the batteries that are located in the XR Frame.

This condition is a communication issue only, and in no way affects the function of the UPS if it were to go on battery. In that event the UPS goes on battery, the runtime will be recalculated based on the on the additional ampacity provided by the Extended Run Frame.

Resetting the communication card on the Extended Run Frame (SYXRCC) will alleviate this communication issue. Please following the following steps in resetting the SYXRCC on the Symmetra Extended Run Frame:

1) Disconnect the communication cable(s) in the SYXRCC located in the back of the Symmetra Extended Run Battery Frame and wait for the green status light to go off.

2) Disconnect the communication cable(s) from the communications card by unscrewing the top right hand thumbscrew on the SYXRCC so that the micro-latch that is being held by that thumbscrew is unseated.

3) Reseat the micro-latch on the SYXRCC and screw in the thumbscrew back into the top right-hand corner of the SYXRCC.

4) Reconnect the communication cable(s) in the back of the SYXRCC and acknowledge the return of the green status light within 60 seconds the UPS will recognize the additional batteries and adjust the runtime value accordingly to include the batteries located in the Extended Run Frame.


At this point the "E3" message should no longer be flashing on the XR Frame and on the PowerView you will see a message indicating "Number of Battery Modules Increased".

If for any reason this error message reoccurs, please contact APC Technical Support at 800-800-4APC and a technician will be able to assist you.
-----------------------------------------------------------------------------------------------------------------
Basically this is a communications fault. The issue could lie either with the XR Comm card, the cable from the Symmetra to the XR frame, or the intelligence module of the Symmetra. These are the most common causes and I would advise you to call into APC tech. support as the troubleshooting is usually reactive in terms of steps and can be lengthy sometimes.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Reply 1
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

0 Likes
0
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:32 AM . Last Modified: ‎2024-03-19 01:25 AM

From a public APC Knowledge Base:

The "E3" error message on the Symmetra XR Frame is an indication of lost communication between the Symmetra Power Array and the Symmetra Extended Run Battery Frame. This error message will cause a fault LED on the PowerView on the Symmetra Power Array and will result in the loss of communication between the two frames where the Power Array will not be able to recognize the batteries that are located in the XR Frame.

This condition is a communication issue only, and in no way affects the function of the UPS if it were to go on battery. In that event the UPS goes on battery, the runtime will be recalculated based on the on the additional ampacity provided by the Extended Run Frame.

Resetting the communication card on the Extended Run Frame (SYXRCC) will alleviate this communication issue. Please following the following steps in resetting the SYXRCC on the Symmetra Extended Run Frame:

1) Disconnect the communication cable(s) in the SYXRCC located in the back of the Symmetra Extended Run Battery Frame and wait for the green status light to go off.

2) Disconnect the communication cable(s) from the communications card by unscrewing the top right hand thumbscrew on the SYXRCC so that the micro-latch that is being held by that thumbscrew is unseated.

3) Reseat the micro-latch on the SYXRCC and screw in the thumbscrew back into the top right-hand corner of the SYXRCC.

4) Reconnect the communication cable(s) in the back of the SYXRCC and acknowledge the return of the green status light within 60 seconds the UPS will recognize the additional batteries and adjust the runtime value accordingly to include the batteries located in the Extended Run Frame.


At this point the "E3" message should no longer be flashing on the XR Frame and on the PowerView you will see a message indicating "Number of Battery Modules Increased".

If for any reason this error message reoccurs, please contact APC Technical Support at 800-800-4APC and a technician will be able to assist you.
-----------------------------------------------------------------------------------------------------------------
Basically this is a communications fault. The issue could lie either with the XR Comm card, the cable from the Symmetra to the XR frame, or the intelligence module of the Symmetra. These are the most common causes and I would advise you to call into APC tech. support as the troubleshooting is usually reactive in terms of steps and can be lengthy sometimes.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of