Posted: 2024-12-02 07:08 AM
Good morning everyone, a question please. I have installed a SMART UPS RC3000, it is connected to my local network, and I need to monitor it, and I want to install the POWERCHUTE software for business, but it asks me for a UPS parameter; what does UPS mean? And which one corresponds to this UPS model.
Please, your help.
Thank you.
Luis
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-03 06:19 PM
The Model number may be incorrect the UPS model number should start with SMT SMX or SRT and please send screen shot of the port used the PowerChute businesse edition is now replaced by the PowerChute serial Shutdown and it should be used with the serial port or USB port of the UPS
Here is a sample port The model is a SMT3000C
The Green Port SmartConnect Port is used for Cloud monitoring on smartconnect.apc.com and requires a subscription and the serial and USB port can be used with either Powerchute Business Edition or Power Chute serial shutdown which is free to use.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.