Smart-UPS 750 Problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 750 Problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
12
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

Smart-UPS 750 Problem

I got new Smart UPS 750VA yesterday. I connected my Workstation and LCD. The load on the UPS is around 65-66%. Yet when i cut the power to the ups the workstation dies instantly and there is some hissing like noise form the ups for a second. The power is still fed from the ups because the likghts on the workstation are on. If i then try to turn the workstation on while ups is still running from battery it turns on ok but dies of after around 10 sec (when the load rises). When i tried to boot it off battery without lcd its able to boot allright, but if i cut the power to that configuration the workstation still dies on me.
i Tried sifferent PC (which gives about 20% load) and its working allright with same lcd attached.

So the question is what might be the problem here. Is the UPS too weak for my workstation and i should get it replaced for larger one, or is the UPS faulty and its not giving enough power under load while on battery power and i should replace it for another one?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

Just to check the load. Could you connect a non-computer load @ 400W ( let us say classic electric lamps) or more ? Will UPS support the load?

From your data it looks like the PSU draws more then 500W ( please note the efficiency of the PSU)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
0
1463
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

during normal operation the 440 gives about 20% and 620 about 65% but its not the same hardware theyre powering up but ill try to connect thae 620 to the lower end PC and see how it goes then. Ill let u know asap.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

thanks for cealring that up, too bad i didnt know that sooner πŸ™‚ ill get bigger ups then as it seems it works perfectly fine with 400W PSU i have around so the UPS itself must be ok.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

Does your workstation have an power factor corrected power supply? If so, the UPS may be grossly undersized for your needs.

Also you might want to check with the workstation's PSU manufacturer to find out if a 2-4 millisecond transfer time is acceptable from the UPS. If not, there's the problem, and you'll need something like an SURTA1500XL.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

Yes i checked on the manufacturer site and it appears that this PSu have Active PFC system installed. The PSU is rated at 620W but it only draws around 260-280. So i should get UPS with watt ratings over 620 then? Because i relly dont know what that active PFC system really means in terms of power consumption and needs when it comes to UPS workings, and why would it make any problems when the load is well below the rated power output of the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:34 AM

Hi....here's what happens when you use an undersized UPS and a PFC power supply.

Upon transfer to battery (the mere 2-4 milliseconds), the capacitors in the PFC PSU discharge to keep the system up and running. As soon as the UPS is back on battery and the PSU sees sufficient power, it will attempt to recharge all the capcitors simultaneously. This is where the maximum draw of power comes from the PSU specs. They'll reach 620 and overload the UPS or just completely drain the battery with such an increase in power draw and a decrease in runtime available.


So yeah, you would need a UPS that is capable of handling 620W plus everything else you're plugging into it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

The Notorious K.M.P. wrote:
Hi....here's what happens when you use an undersized UPS and a PFC power supply.

Upon transfer to battery (the mere 2-4 milliseconds), the capacitors in the PFC PSU discharge to keep the system up and running. As soon as the UPS is back on battery and the PSU sees sufficient power, it will attempt to recharge all the capcitors simultaneously. This is where the maximum draw of power comes from the PSU specs. They'll reach 620 and overload the UPS or just completely drain the battery with such an increase in power draw and a decrease in runtime available.


So yeah, you would need a UPS that is capable of handling 620W plus everything else you're plugging into it.
Kevin,
The bulk storage capacitor holds the PC in both PFC and non-PFC power supplies. The type is irrelevant.
The maximum watt specs on PSU is supposed to represent the MAXIMUM OUTPUT. It has nothing to do with surge power.

OP,
I'm not sure how accurately the load tracking works on APC UPS though. What did you use to measure you're only drawing around ~250W?

What are the specs on your PC? The power supply size tells you nothing about the power consumption, but it merely represents the maximum power the PSU can supply.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

im using:
http://www.pentagram.pl/produkty/zasilacze_do_obudow/pentagram_silent_force_psf_620_a12s_p_9005_2
it have that nice little feature which is LCD display showing current power draw of PSU and it is usually between 250-300W thats why i knew what amount of power load it generates, and thats why i thought 500W UPS should be more than enough to feed ~400W power load.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

Hello, zipper,
Coud you connect other load and check how UPS works?
For eg. just LCD while computer works from other power line?
Also, please try to install software to see data from UPS ( battery voltage, Runtime remaining,
Bat Capacity etc)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

yeah i tried different load. 400W PSU with active PFC aswell. it was running at ~20% load of the UPS and cutting power to UPS didnt kill the PC.
Power chute with my main workstation connected said it was about 65% load with 6 minutes runtime.
battery was just over 24V. It was fully charged aswell. Selftest passed without problems.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

What will be the difference between the loads if the 400W PSU with active PFC aswell?
Any difference?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

ok i tested the bigger workstation connected to 440W active pfc psu (the one that worked fine while supplying power to older one) and the effect was the same. i cut the power, workstation dies, strange whistling sound from ups for about a second. im attaching logs from 2 trys i did.i hope someone can tell me if the ups should be able to pull that off (the 440W of the psu is well within 500@ ups rating now and nothing else was connected to it) and with lower load on the same psu it worked fine.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

0 Likes
0
1464
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 08:35 PM . Last Modified: β€Ž2024-03-15 01:33 AM

Just to check the load. Could you connect a non-computer load @ 400W ( let us say classic electric lamps) or more ? Will UPS support the load?

From your data it looks like the PSU draws more then 500W ( please note the efficiency of the PSU)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore