Powerchute and Vmware

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute and Vmware
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
9
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

Powerchute and Vmware

I have a scenario that i need assistance with. And i am aware it is not supported.. just want to either get rid of it or try and get it to worl.

I have running VmWare 3.0.2 and want to try and get parachute installed on the server, i have done the documentation from APC and know about the firewall ports that need to be opened as well. This is done and is successful on one of the servers, when i went to do it on another server it seems someone has installed it already, but when i try and login to the server using the web browser (http://servername:3052/) it asks for a user name and password which i have no idea what it is.
1. How do i reset it, i have already uninstalled the software and even removed the firewall ports from the server and it seems that the application is still running on the server, because even after removing the ports from the firewall and uninstalled the program with rpm -e pcns and i go back through the browser powerchute is still asking for a password and user id, but i thought i uninstalled it? Any one know whats going on?
2. How can i change the password for powerchute on the esx server? I have no idea how to do that..

Wayne

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

thats the thing, you will need to figure the timing on that unfortunately. with powerchute network shutdown, it gets the signal to shutdown from the network management card that you need to have installed on your UPS. so on both - the powerchute and the management card, you can set certain delays. for example, you can have one of the virtual machines shutdown after the UPS has been on battery for 5 minutes (or other types of events too).

so you will have to stagger them by having them shutdown based on certain events so that they all dont shutdown when the UPS runs out of battery and run out of time.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

I have a scenario that i need assistance with. And i am aware it is not supported.. just want to either get rid of it or try and get it to worl.

I have running VmWare 3.0.2 and want to try and get parachute installed on the server, i have done the documentation from APC and know about the firewall ports that need to be opened as well. This is done and is successful on one of the servers, when i went to do it on another server it seems someone has installed it already, but when i try and login to the server using the web browser (http://servername:3052/) it asks for a user name and password which i have no idea what it is.
1. How do i reset it, i have already uninstalled the software and even removed the firewall ports from the server and it seems that the application is still running on the server, because even after removing the ports from the firewall and uninstalled the program with rpm -e pcns and i go back through the browser powerchute is still asking for a password and user id, but i thought i uninstalled it? Any one know whats going on?
2. How can i change the password for powerchute on the esx server? I have no idea how to do that..

Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

this will shutdown the bare metal VMWare ESX server itself. if you want to shut down the virtual machines, you will have to install powerchute network shutdown invidually on those virtual machine operating systems.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

you want to make sure that you stopkill the service completely then uninstall. so, i'd recommend listing all the running services and finding the ID to kill.

there is no way to reset the password. you'd have to completely uninstall/reinstall the software and install it with a new password.

since you said you did "rpm -e pcns" you must be talking about powerchute network shutdown, rather than powerchute business edition. worst case, if you still cant get it to uninstall, we should be able to get you some manual uninstall instructions for you if we need to go that route.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

Thank you for your responce, the problem is that i do not see any services running, yet i can still open http://servername:3052
I cannot see anything that looks like apc or powerchute that is running. Any assistance would be appreciated.

I did get some information from apc directly to uninstall the software and after following the documentation i did not find any trace of the software.

Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

do you have any case/incident numbers from APC so I can look it up to see what directions were provided? I dont want to have them posted on the forum but i want to make sure that you received the correct instructions.

silly question but there is no chance that you are opening up the wrong server name on the link, is there?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

C1-707238416

I just did a netstat -tulpn and found that port 3052 was JAVA, once i killed that PID i cannot open the http:\\myserver:3052 with is the powerchute web page. However this doesnt answer why it comes up anyways even after uninstalling the software.

And yes i am actually on the esx server, i checked it over and over just to make sure i was on it, this was baffeling to me as well as i thought i was on the wrong server but i am not i know i am on the right server.

What i wonder is why it still pops up a web page for powerchute on http:\\myserver:3052.

Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:34 PM . Last Modified: ‎2024-03-15 01:34 AM

ok-

i found those instructions you were sent which should be ok.

the top part just deals with powerchute business edition. you should have started from mid-way down the instructions which starts:

If you are removing PCNS from any Linux or Suse System...

also, PCNS uses java so it makes sense it was a java process. to me, it just seems like we missed something while uninstalling.

just to clarify - after looking up your case, i cant determine whether you installed PCNS 2.2.1 or 2.2.3. I see you were provided the link to 2.2.1. regardless, ESX is on the compatibility chart for PCNS 2.2.3 so that should work when we figure this out - but what version did you install that is stuck on there?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

Can youtell me then how does the ESX server know when to actually power down? If there are 20 Vm's and they take different times to shut down, how does the ESX box know that all the VM's are down properly then its ok to shut down the ESX server itself?


Wayne

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

0 Likes
0
1149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:35 PM . Last Modified: ‎2024-03-15 01:34 AM

thats the thing, you will need to figure the timing on that unfortunately. with powerchute network shutdown, it gets the signal to shutdown from the network management card that you need to have installed on your UPS. so on both - the powerchute and the management card, you can set certain delays. for example, you can have one of the virtual machines shutdown after the UPS has been on battery for 5 minutes (or other types of events too).

so you will have to stagger them by having them shutdown based on certain events so that they all dont shutdown when the UPS runs out of battery and run out of time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of