Smart UPS 5000 and HP R3000XR advice

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 5000 and HP R3000XR advice
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
8
2133
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

Smart UPS 5000 and HP R3000XR advice

Hi,

Basically we had a power blip, the usual light flicker from maybe a storm etc (high voltage/surge/spike not sure what it was) and the 5000 had literally switched off.. it sat there with every light flashing at the same time. The entire rack was off... I switched the UPS off using the power button, then back on and it all went up and started working again! The batteries were replaced maye 2 years ago, its at about 10-20% load and all LED's are green with the battery fully charged. It did not error on the original spikes though, only one of the power spikes seems to of caught it out.

I would assume this was just a UPS issuse and it was broken, BUT the HP R3000XR in a different rack (on the next spike later on) simply beeped and a red light appeared for a second, the entire cabinet of servers rebooted and now its back up and all green lights again... I find it really odd two brands of UPS had simulat symptoms. They have always been 100% fine from what I can remember with all power issues.

The 3rd HP R3000XR had no issues (only at 20% load).

For the moment, as the more important servers have 3 psu's, ive connected each PSU to a different UPS to maximize uptime, assuming the chances of 2 failing at once are much lower.

Any Ideas?

Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

The UK, so voltage is 240v.

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

can you tell us what the current battery voltage of the Smart UPS is? either via the network management card or software or even a voltmeter?

all the LEDs flashing on the front of the UPS indicate a DC bus problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

Hi!

When I checked yesterday, the status was as follows :-

Input V: 244.4
frequency: 50hz
max line: 247
min line: 243.1

Output v: 244.4
Output Frequency: 50hz
Load Power: 030.1% watts


Battery Capacity: 100%
Runtime Remaining: 33 minutes
Battery V: 55.05 VDC
Seld test results: passed
Clibration Result/date: Uknown



The log says:-

09/25/2006 12:09:28 System: Web User apc logged in from
09/25/2006 10:14:06 UPS: Passed internal self-test.
09/25/2006 10:13:56 UPS: Turned on.
09/25/2006 10:05:00 UPS: Failed internal diagnostic self-test.
09/25/2006 10:04:46 UPS: Turned off.
09/24/2006 18:09:40 UPS: Passed internal self-test.
09/24/2006 05:23:58 UPS: Returned from SmartTrim.
09/23/2006 19:22:26 UPS: Enabled SmartTrim; high incoming line voltage.



The date is wrong I discovered, but the problem happened about 10am on 25th (by these dates).


From what i remember, every light was flashing in sync on and off.


Thanks for you help, its much appreciated!

Message was edited by: leonr

Message was edited by: leonr

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

what is the exact model on this UPS? can you grab it from the back of the UPS on the little white sticker?

issue number one i see is that if this is an SUA5000RMT5U or SU5000RMT5U, that is supposed to be fed an input of nominal 208v and not 240v. it looks like it is one of those models because it has Trim. please confirm if you dont mind.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

Hi!

Again thanks for the reply πŸ™‚

The model is "SU5000RM15U" or an I , not sure.

Thanks!

Message was edited by: leonr

Message was edited by: leonr

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

ok its probably SU5000RMI5U.

what country are you using this in?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:38 AM

hmm ok everything looks good status wise that you pasted. it seems to me for some reason that there was a DC bus problem on the UPS so it turned off and thus, all of the LEDs started flashing. unfortunately i am not sure WHY it happened..

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

0 Likes
0
2129
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

No problem!

I appreicate that you looked into it for me πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

0 Likes
0
2130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-28 10:19 PM . Last Modified: β€Ž2024-03-14 04:37 AM

The UK, so voltage is 240v.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore