Smart UPS 5000 and HP R3000XR advice
Hi,
Basically we had a power blip, the usual light flicker from maybe a storm etc (high voltage/surge/spike not sure what it was) and the 5000 had literally switched off.. it sat there with every light flashing at the same time. The entire rack was off... I switched the UPS off using the power button, then back on and it all went up and started working again! The batteries were replaced maye 2 years ago, its at about 10-20% load and all LED's are green with the battery fully charged. It did not error on the original spikes though, only one of the power spikes seems to of caught it out.
I would assume this was just a UPS issuse and it was broken, BUT the HP R3000XR in a different rack (on the next spike later on) simply beeped and a red light appeared for a second, the entire cabinet of servers rebooted and now its back up and all green lights again... I find it really odd two brands of UPS had simulat symptoms. They have always been 100% fine from what I can remember with all power issues.
The 3rd HP R3000XR had no issues (only at 20% load).
For the moment, as the more important servers have 3 psu's, ive connected each PSU to a different UPS to maximize uptime, assuming the chances of 2 failing at once are much lower.
Any Ideas?
Thanks!
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions

Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
The UK, so voltage is 240v.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
can you tell us what the current battery voltage of the Smart UPS is? either via the network management card or software or even a voltmeter?
all the LEDs flashing on the front of the UPS indicate a DC bus problem.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
Hi!
When I checked yesterday, the status was as follows :-
Input V: 244.4
frequency: 50hz
max line: 247
min line: 243.1
Output v: 244.4
Output Frequency: 50hz
Load Power: 030.1% watts
Battery Capacity: 100%
Runtime Remaining: 33 minutes
Battery V: 55.05 VDC
Seld test results: passed
Clibration Result/date: Uknown
The log says:-
09/25/2006 12:09:28 System: Web User apc logged in from
09/25/2006 10:14:06 UPS: Passed internal self-test.
09/25/2006 10:13:56 UPS: Turned on.
09/25/2006 10:05:00 UPS: Failed internal diagnostic self-test.
09/25/2006 10:04:46 UPS: Turned off.
09/24/2006 18:09:40 UPS: Passed internal self-test.
09/24/2006 05:23:58 UPS: Returned from SmartTrim.
09/23/2006 19:22:26 UPS: Enabled SmartTrim; high incoming line voltage.
The date is wrong I discovered, but the problem happened about 10am on 25th (by these dates).
From what i remember, every light was flashing in sync on and off.
Thanks for you help, its much appreciated!
Message was edited by: leonr
Message was edited by: leonr
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
what is the exact model on this UPS? can you grab it from the back of the UPS on the little white sticker?
issue number one i see is that if this is an SUA5000RMT5U or SU5000RMT5U, that is supposed to be fed an input of nominal 208v and not 240v. it looks like it is one of those models because it has Trim. please confirm if you dont mind.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
Hi!
Again thanks for the reply 🙂
The model is "SU5000RM15U" or an I , not sure.
Thanks!
Message was edited by: leonr
Message was edited by: leonr
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
ok its probably SU5000RMI5U.
what country are you using this in?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:38 AM
hmm ok everything looks good status wise that you pasted. it seems to me for some reason that there was a DC bus problem on the UPS so it turned off and thus, all of the LEDs started flashing. unfortunately i am not sure WHY it happened..
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
No problem!
I appreicate that you looked into it for me 🙂
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:19 PM . Last Modified: 2024-03-14 04:37 AM
The UK, so voltage is 240v.
Thanks!