Smart-UPS 5000 (SUA5000RMT5U) 5 Green leds still blinking after Battery Replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 5000 (SUA5000RMT5U) 5 Green leds still blinking after Battery Replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Timmm
Crewman Timmm
Crewman

Posted: ‎2025-02-20 01:00 AM

0 Likes
4
342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-20 01:00 AM

Smart-UPS 5000 (SUA5000RMT5U) 5 Green leds still blinking after Battery Replacement

Hello,

I've just replaced the 4 Batteries on my Smart-UPS 5000 (SUA5000RMT5U) yesterday.

Today, after 18 hours of charging, the 5 green leds are still blinking.

I did a Self-Test this morning and it passed but I still have a Critical Alarm: Discharged Battery
I also have this message in the logs: UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.

But, the UPS Status is:
Load in Watts: 26%
Battery Capacity: 100%
Runtime Remaining: 3min

My questions are:
5 Green blinking leds means that UPS Batteries are not fully charged ?
If so, should I have to wait longer for Batteries to be fully charged ?
If Batteries are not fully charged, why Battery Capacity shows 100% ?
Should I have something else to do after Batteries Replacement ?

Thanks in advance for your help
Tim


Here are the full logs since yesterday

20.02.2025 09:32:48 UPS: Passed a self-test.
20.02.2025 09:32:42 UPS: A low battery condition no longer exists.
20.02.2025 09:32:42 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
20.02.2025 09:32:32 UPS: The battery power is too low to continue to support the load; the UPS will shut down if input power does not return to normal soon.
20.02.2025 09:32:32 UPS: A discharged battery condition no longer exists.
20.02.2025 09:32:32 UPS: Started a self-test.
20.02.2025 09:32:32 UPS: A faulty battery no longer exists.
19.02.2025 17:14:12 UPS: The battery is now installed.
19.02.2025 17:13:32 UPS: The battery is not installed properly.
19.02.2025 17:12:49 UPS: The battery is now installed.
19.02.2025 17:08:44 UPS: The battery is not installed properly.
19.02.2025 11:57:56 UPS: Self-Test Failed
19.02.2025 11:57:42 UPS: At least one faulty battery exists.
12.02.2025 20:24:08 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
12.02.2025 20:23:52 UPS: The output power is now turned on.
12.02.2025 18:47:30 UPS: The output power is turned off.The output power is turned off due to a low battery.
12.02.2025 18:47:29 UPS: Restored the local network management interface-to-UPS communication.
12.02.2025 18:47:15 System: Network service started. System IP is x.x.x.x from manually configured settings.
12.02.2025 18:46:59 System: Warmstart.
12.02.2025 18:35:26 UPS: The output power is turned off.
12.02.2025 18:35:26 UPS: A discharged battery condition no longer exists.

  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Timmm
Crewman Timmm
Crewman

Posted: ‎2025-02-21 02:04 AM

In response to Timmm
0 Likes
0
293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 02:04 AM

OK. It finally works.

I did a Runtime Calibration that I stopped after 5 min.

Then the Battery Capacity change to 0%

Now it's charging. The Battery Capacity is at 50% after 2 hours.

I think you have to do a Battery Calibration after changing them.

Otherwise the UPS is not aware that Batteries has been changed and it is still calibrated on old low Batteries Voltage. So it said that it is at 100% and was not charging them.

The Battery Calibration has reset this value and now the UPS is charging the Batteries.

Thanks for your help

 

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Teken
Spock Teken
Spock

Posted: ‎2025-02-20 04:48 AM

0 Likes
2
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-20 04:48 AM

You’ll need to wait for the battery cartridge to fully charge for 72 hours. Once the battery is 100% SOC. Verify the same with a multimeter and report back the surface voltage.

 

You must remove and let sit outside of the unit and record the battery voltage at the time of removal and 24-72 hours later.

 

Report the measurements here.

 

Afterwards reinstall the battery cartridge and update the battery installation date. Follow up with manually initiating a Self Test.

 

Once complete let the battery cartridge return to 100% SOC (State of Charge). Finalize by manually initiating a Battery Calibration with at least 30% attached load.

 

Let the system complete this procedure and recharge back up. The battery indicator should be more accurate and in time will display 100% charge. 

The load LED’s should also stop flashing after this procedure has been completed.

 

NOTE: If the above steps do not resolve the issue you may try the Brain Dead procedure as out lined here:

 

https://www.apc.com/us/en/faqs/FA156611/

Questions Ask . . . 👍

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Timmm
Crewman Timmm
Crewman

Posted: ‎2025-02-21 12:22 AM

In response to Teken
0 Likes
1
299
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 12:22 AM

Hello,

Thank you for the clear procedure.

I come back to you when it's done.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Timmm
Crewman Timmm
Crewman

Posted: ‎2025-02-21 02:04 AM

In response to Timmm
0 Likes
0
294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 02:04 AM

OK. It finally works.

I did a Runtime Calibration that I stopped after 5 min.

Then the Battery Capacity change to 0%

Now it's charging. The Battery Capacity is at 50% after 2 hours.

I think you have to do a Battery Calibration after changing them.

Otherwise the UPS is not aware that Batteries has been changed and it is still calibrated on old low Batteries Voltage. So it said that it is at 100% and was not charging them.

The Battery Calibration has reset this value and now the UPS is charging the Batteries.

Thanks for your help

 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Timmm
Crewman Timmm
Crewman

Posted: ‎2025-02-21 02:08 AM

0 Likes
0
291
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 02:08 AM

OK. It finally works.

I did a Runtime Calibration.

Then the Battery Capacity change to 0%

Now it's charging. The Battery Capacity is at 50% after 2 hours.

I think you have to do a Battery Calibration after changing them.

Otherwise the UPS is not aware that Batteries has been changed and it is still calibrated on old low Batteries Voltage. So it said that it is at 100% and was not charging them.

The Battery Calibration has reset this value and now the UPS is charging the Batteries.

Thanks for your help

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of