Compressor Drive fault

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Compressor Drive fault
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
4
3370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Compressor Drive fault

Dear team,

We are using acrp102 cooling unit, suddenly it is showing alarm of Compressor Drive fault but it becomes normal after automatic/forceful restart.please find the attached logs and guide us.

Your prompt response will be highly appreciated.

Regards

MS

Attachments
Labels
  • Labels:
  • Racks, Rack Accessories, & Cooling
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
1
3368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Hello Muhammad.

From the event logs I see the unit is experiencing a lot of cold starts. Unless this is someone manually flipping the breaker on the unit, I would suggest checking the incoming power to the unit. If there are fluxuations in the power coming in, this would cause the cold starts and could cause the compressor drive alarms.

A System Coldstart event indicates that the NMC (Network Management Card) has just been powered and has completed startup.

  • Power interruption to the NMC - If a device powering the NMC suffers an interruption of power, the NMC will restart when power is reapplied to that device.

The alarm codes on the vfd that you sent in have to do with the high head pressure switch. You should check that the condenser is working properly to get rid of the heat and check the connections to and from the high head pressure switch.

Thank you

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
1
3369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Hello Muhammad.

From the event logs I see the unit is experiencing a lot of cold starts. Unless this is someone manually flipping the breaker on the unit, I would suggest checking the incoming power to the unit. If there are fluxuations in the power coming in, this would cause the cold starts and could cause the compressor drive alarms.

A System Coldstart event indicates that the NMC (Network Management Card) has just been powered and has completed startup.

  • Power interruption to the NMC - If a device powering the NMC suffers an interruption of power, the NMC will restart when power is reapplied to that device.

The alarm codes on the vfd that you sent in have to do with the high head pressure switch. You should check that the condenser is working properly to get rid of the heat and check the connections to and from the high head pressure switch.

Thank you

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
3368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Thanks alot

Reply

Link copied. Please paste this link to share this article on your social media post.

shahzad.engr123_apc
Lieutenant JG shahzad.engr123_apc
Lieutenant JG

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

0 Likes
0
3368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 01:25 AM . Last Modified: ‎2024-03-18 11:30 PM

Dear L2SupportServices,

But there is another cooling unit installed in same location which is working fine, there is no error on that unit.

Regards

MS

Reply

Link copied. Please paste this link to share this article on your social media post.

msg4t
msg4t
Cadet

Posted: ‎2025-02-21 04:29 AM

In response to BillP
0 Likes
0
240
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-21 04:29 AM

I have a piece of equipment that periodically gives the following alarm: "compressor drive fault". When the unit is checked, a reset is performed and the equipment returns to operation. Electrical inspection of the equipment's power supply has been done, and everything appears normal. What could cause this alarm? Could it be an indication of a fault in the compressor or the drive? An alarm for speed was also identified on the inverter. This happens over long periods of time, occurring every few weeks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of