Smart-UPS 5000 RM / Batteries need immediate replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 5000 RM / Batteries need immediate replacement
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
7
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Smart-UPS 5000 RM / Batteries need immediate replacement

Hi All,

I have a problem with a "Smart-UPS 5000 RM" (SU5000R5IBX120). Some days ago I got a notification that the batteries need immediate replacement. I have replaced the batteries but the battery alarm LED is still red and any self test fails. On the weekend I have calibrated the UPS successfully but the LED remains red. After that I have disconnected the UPS and powered off. After powering on the self test was successfully. Today I started a self test manually but it failed again with "Batteries need immediate replacement".

The battery is loading successfully up to 100 %.

 

Any idea or help is highly appreciated. 

Best Regards - Bernd

 

  

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 5000
  • batteries
  • immediate
  • need
  • replacement
  • rm
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Yes, I just tested this with an SUA3000 with a 9617.

Log in and log out again. When the card says "Loggin out." Press "Y".

Any UPSLINK command will be answered. Any character not in the UPSLINK command set will cause the card to request a login, and you must log in and out again to get it back into listening for UPSLINK command mode.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

Brad,

this helped me a lot. You saved my evening. I could check the battery constant. It is 91 as it should be. I am afraid I have to start looking for a new UPS.

Thanks a lot for your support - Bernd

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Hello Bernd, 

What is the serial number of your UPS? Also, did you replace the battery with genuine a APC battery or a 3rd party battery?

If your UPS is close or above 10 years old, the problem could be the UPS itself is having a problem recognizing the new battery. If you used a 3rd party battery, our UPSs are meant to only work with APC batteries and that could be the reason the UPS is still reporting it needs a new battery. 

Regards, 

Nicole 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Hi Nicole,

the serial number of the UPS is AS0725160389. The serial number of the genuine APC batteries is 7A1649L16027.

APC.DE advised me to check and adjust the battery constant. Do you think this is worth trying ?

Best Regards - Bernd

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

You could certainly *check* the battery constant to see if it is plausible without disrupting anything.

Just hook a serial cable up to the UPS, set it for 2400,8,n,1.

Type Y and it should respond with SM. If it does that, type 0 and it will respond with the battery constant.

Type R and it should respond with BYE, and you can disconnect.

If it has an NMC you may have to remove it first. I have a 9606 and a 9617 and they both pass the basic UPSLINK commands through on the serial interface, but they block getting it into program mode (not that you need it for checking the battery constant).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Hi Brad,

after connecting the serial cable I landed on the 9617 and was prompted for user id and p/w. Is there a way to check the battery constant w/o power down the UPS and removing the 9617 ?

Best Regards - Bernd

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:13 AM . Last Modified: ‎2024-03-18 02:36 AM

Yes, I just tested this with an SUA3000 with a 9617.

Log in and log out again. When the card says "Loggin out." Press "Y".

Any UPSLINK command will be answered. Any character not in the UPSLINK command set will cause the card to request a login, and you must log in and out again to get it back into listening for UPSLINK command mode.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

Brad,

this helped me a lot. You saved my evening. I could check the battery constant. It is 91 as it should be. I am afraid I have to start looking for a new UPS.

Thanks a lot for your support - Bernd

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

0 Likes
0
2867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:14 AM . Last Modified: ‎2024-03-18 02:36 AM

Before you trash it. Have a really good look at the battery contacts and the fuses on the battery pack (if they are on the pack themselves).

The fact it passed a calibration and passed a power-on self test indicates the hardware is/was fundamentally ok. The batteries are new and should be fine.

The UPS performs 2 tests for the batteries. One is a periodic pause in the charger. If the voltage holds up it says "I have a battery present", and the other is the periodic self test. That actually starts the inverter and transfers the load to battery to check the charged but loaded voltage on the battery. A dicey connection or dud fuse could easily cause those symptoms.

Does the unit actually transfer to battery when you try a self-test? Does it hold up if you pull the mains? (If it does both of those then don't bother reading further).

If you have a volt-meter, pull the batteries out and measure the voltage on the connectors on the UPS. They are connected in series so one will have positive, the other negative and the remaining 2 pins will be connected together. Some of the larger UPS I've worked on have had the battery fuse internal to the unit. Make sure you see ~55V on those terminals. The UPS will quite happily tell you the float voltage is fine with no battery connected.

Fuses are pretty robust, but they do fail occasionally. Make sure the pins on the connectors are clean. Again, they are self-wiping and pretty robust but stuff happens.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore