I have two Windows 2003 Standard Servers, one Redhat Enterprise Server and a Debian Server and one Smart-UPS 3000 RM DL3 (according to PowerChute 7.0.5).
I have the UPS connected to one of my Windows 2003 Servers via Serial and have installed the PowerChute 7.0.5 Agent/Server/Console on this server.
In the event of a power failure I would like the UPS to signal my connected server which will then signal the other three servers on my network to shut down. From the reading I have done I don't appear to be able to do this using the PowerChute Agents.
Am I correct in saying I either need to get a Share-UPS Devices to share one serial connection with multiple servers and install the PowerChute Agent on each server or I need to get a APC Network Management Card, install it into my Smart-UPS 3000, connect it to the network and then install the 'Network Shutdown' software?
Am I on the right track here?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
you'd have to look into getting an [AP9607 interface expander|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9607] to use in the UPS accessory smart slot as well as the correct AS400 signaling cables.
here is some info on the cables:
• 940-0006 – AS/400 - There are two cables in this box. One cable has a DB15 for attaching to very old (and much larger) AS/400 servers. The other cable (the only one we ever use) has a DB9 for attaching the AS/400. Both obviously have a DB9 on the other end that attaches to the UPS.
• AP98274 – i5, Power 5/6/7 - This is for these servers going back only about 5 years, starting with the i5 Model 520. Since then there has been Power 6 and just this summer Power 7 lines of servers. They all use this newer cable.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
We are using Debian and Redhat Enterprise 4.
We only have PowerChute Basic Edition. From what I have read the Network solution doesn't require us to purchase any software.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
Hello,
Yes, Powerchute Network Shutdown is a free download off the APC website.
The supported versions for Powerchute Network Shutdown are in the link below:
http://sturgeon.apcc.com/techref.nsf/docID/56B57F3084E605918525720A005BC585/$FILE/990-3060-EN.pdf
The supported versions of Powerchute Business Edition are in the link below;
http://sturgeon.apcc.com/techref.nsf/docID/A625AF078E3BB20686257209005EBE40/$FILE/990-3058-EN.pdf
Have a nice weekend.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
I have two Windows 2003 Standard Servers, one Redhat Enterprise Server and a Debian Server and one Smart-UPS 3000 RM DL3 (according to PowerChute 7.0.5).
I have the UPS connected to one of my Windows 2003 Servers via Serial and have installed the PowerChute 7.0.5 Agent/Server/Console on this server.
In the event of a power failure I would like the UPS to signal my connected server which will then signal the other three servers on my network to shut down. From the reading I have done I don't appear to be able to do this using the PowerChute Agents.
Am I correct in saying I either need to get a Share-UPS Devices to share one serial connection with multiple servers and install the PowerChute Agent on each server or I need to get a APC Network Management Card, install it into my Smart-UPS 3000, connect it to the network and then install the 'Network Shutdown' software?
Am I on the right track here?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
My client has two IBM AS400 9406 model 820 and 810 connected to a single 10KVA APC SMART UPS RT 10000 XL In the event of a power failure I would like the UPS to signal the two AS400s to shut down. Is there a way to do this as I noticed only one serial port at the back of the UPS?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 12:30 PM . Last Modified: 2024-03-15 04:04 AM
you'd have to look into getting an [AP9607 interface expander|http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9607] to use in the UPS accessory smart slot as well as the correct AS400 signaling cables.
here is some info on the cables:
• 940-0006 – AS/400 - There are two cables in this box. One cable has a DB15 for attaching to very old (and much larger) AS/400 servers. The other cable (the only one we ever use) has a DB9 for attaching the AS/400. Both obviously have a DB9 on the other end that attaches to the UPS.
• AP98274 – i5, Power 5/6/7 - This is for these servers going back only about 5 years, starting with the i5 Model 520. Since then there has been Power 6 and just this summer Power 7 lines of servers. They all use this newer cable.
Link copied. Please paste this link to share this article on your social media post.