Smart UPS 3000 XL, run on partial battery pack?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 3000 XL, run on partial battery pack?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
2
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:55 AM . Last Modified: ‎2024-03-13 11:39 PM

Smart UPS 3000 XL, run on partial battery pack?

Hello:

I've got a Smart UPS 3000 XL (rack mount). The batteries are going on 5 years old, so I would like to recondition them with a separate battery conditioner. I pulled the battery pack and noticed that it has two 48V battery arrays connected in parallel (4 12V batteries for each of the two arrays, for a total of 8 batteries). Will it hurt anything to remove one of the arrays (4 batteries), and run the UPS on the remaining array of 4 batteries? It will take the conditioner about 3 weeks to complete so I want to make sure this won't harm the 4 batteries left in the UPS unit for this amount of time. This should maintain the 48 volts, but I'm assuming that the total runtime on battery will be lower, which is not a big deal at the moment. I just want to confirm that this won't cause the UPS to overcharge or do anything to the 4 remaining batteries since 4 are missing. I noticed that when I removed the 4 batteries, the battery meter on the front of the UPS unit was at 3 out of 5 bars, then the next day it was at a full 5 out of 5 bars.

Thank you for your help!!

--
Chris

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

Hello:

I've got a Smart UPS 3000 XL (rack mount). The batteries are going on 5 years old, so I would like to recondition them with a separate battery conditioner. I pulled the battery pack and noticed that it has two 48V battery arrays connected in parallel (4 12V batteries for each of the two arrays, for a total of 8 batteries). Will it hurt anything to remove one of the arrays (4 batteries), and run the UPS on the remaining array of 4 batteries? It will take the conditioner about 3 weeks to complete so I want to make sure this won't harm the 4 batteries left in the UPS unit for this amount of time. This should maintain the 48 volts, but I'm assuming that the total runtime on battery will be lower, which is not a big deal at the moment. I just want to confirm that this won't cause the UPS to overcharge or do anything to the 4 remaining batteries since 4 are missing. I noticed that when I removed the 4 batteries, the battery meter on the front of the UPS unit was at 3 out of 5 bars, then the next day it was at a full 5 out of 5 bars.

Thank you for your help!!

--
Chris

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:39 PM

0 Likes
0
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:39 PM

Just for the record, I've had half of the batteries removed for about 3 weeks and no issues, while I condition the other half of the batteries. In fact, the self test has passed as the unit has stayed online without any warning lights. Thanks again for the feedback.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:56 AM . Last Modified: ‎2024-03-13 11:38 PM

Hello:

I've got a Smart UPS 3000 XL (rack mount). The batteries are going on 5 years old, so I would like to recondition them with a separate battery conditioner. I pulled the battery pack and noticed that it has two 48V battery arrays connected in parallel (4 12V batteries for each of the two arrays, for a total of 8 batteries). Will it hurt anything to remove one of the arrays (4 batteries), and run the UPS on the remaining array of 4 batteries? It will take the conditioner about 3 weeks to complete so I want to make sure this won't harm the 4 batteries left in the UPS unit for this amount of time. This should maintain the 48 volts, but I'm assuming that the total runtime on battery will be lower, which is not a big deal at the moment. I just want to confirm that this won't cause the UPS to overcharge or do anything to the 4 remaining batteries since 4 are missing. I noticed that when I removed the 4 batteries, the battery meter on the front of the UPS unit was at 3 out of 5 bars, then the next day it was at a full 5 out of 5 bars.

Thank you for your help!!

--
Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore