Smart-UPS 3000 - The battery is not installed properly.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 - The battery is not installed properly.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ICT-UV_apc
Crewman ICT-UV_apc
Crewman

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
9
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Smart-UPS 3000 - The battery is not installed properly.

We have two Smart-UPS 3000, one of them has recently started alerting us with the message "The battery is not installed properly." The battery has been removed and re-fitted but the alert is still present. The firmware on the NMC has also been updated. Could it be that the battery just needs replacing?

Smart-UPS 3000 SMT3000RMI2U (Manufacture date: 12/19/2012)

UPS Network Management Card 2 (AP9631, Firmware v6.4.0)

Any ideas?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • battery
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Hi Bill,

No problem. Glad the battery swap was able to confirm the issue is the battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Hi Bill,

Could you post the full logs? Or at least event.txt/event log and data.txt/data log to see some history on this? We could look at any other events that indicate something other than a battery at its beginning stages of failure. It will also show when the latest battery self test passed as when this fails, it typically reports that it failed and that'd also indicate a bad battery. Maybe that test is due shortly or we can try one manually (but I want to see the logs before I suggest that).

The data log can show us the history of battery capacity and voltage. It could need a battery which is most likely or there is a slim chance the UPS could have a problem "seeing" the battery and it being a UPS problem.

Instructions are downloading the logs are here -> http://www.schneider-electric.us/en/faqs/FA156131 the .tar file is fine as explained there or as I said, individual event and data log.

Reply

Link copied. Please paste this link to share this article on your social media post.

ICT-UV_apc
Crewman ICT-UV_apc
Crewman

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Attached are the event and data files.

I've tried manually performing a self test and the UPS powered off.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Hi Bill,

Had you cleared the event log yesterday? I can't see anything from before yesterday unfortunately.

With what I see, I have no reason to believe that the issue is NOT the battery, especially since you said the UPS turned off when you did a self test. That would be the first logical step to address the issue you've described in my opinion and experience.

Reply

Link copied. Please paste this link to share this article on your social media post.

ICT-UV_apc
Crewman ICT-UV_apc
Crewman

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Yes, I cleared the logs yesterday to try and see what was happening. From email alerts the last succesful self test was on the 22-2-2016 and the code was: 0x0137

I have another UPS of the same type, is it worth swapping the batteries between the two?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Hi Bill,

Ahh, OK. And yes, I think it is worth a try to swap the known good batteries in just for a sanity check before you go ahead to purchase a new pack (since you have it available anyway). On your second UPS, you don't have to turn the UPS off while you do it and can leave it on but it will just beep about the battery being disconnected and have no battery back up functionality with the battery out.

You could swap the known good pack in which I assume is 100% charged from being in the other UPS and run a self test and just confirm you don't see any problems like the constant flood of messages you saw in the log about battery not being installed properly.

Reply

Link copied. Please paste this link to share this article on your social media post.

ICT-UV_apc
Crewman ICT-UV_apc
Crewman

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

No errors for 5 days, so I thought I'd try a self test from the front panel. The UPS remained on but turned off the outputs, and then wouldn't detect the battery again. Logs are attached, I may get timer alter in the week to swap over batteries.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Ahh, yeah sounds like a battery for sure that might be on its way out.

Reply

Link copied. Please paste this link to share this article on your social media post.

ICT-UV_apc
Crewman ICT-UV_apc
Crewman

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Swapped the batteries and the faulty one triggers the same error on the other UPS, the non-faulty detects as normal in the originals UPS. Time to buy a new battery. Thanks Angela. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

0 Likes
0
12592
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 03:35 AM . Last Modified: ‎2024-03-18 04:32 AM

Hi Bill,

No problem. Glad the battery swap was able to confirm the issue is the battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore