Smart-UPS 3000 RM Battery power too low to support the load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 RM Battery power too low to support the load
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

0 Likes
7
1610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

Smart-UPS 3000 RM Battery power too low to support the load

Hello,

We have a Smart UPS 3000 which every couple of days we get the following message appear in the log:

+'Critical - UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.'+

And then we get another message after the above in the same minute:

+'Informational - UPS: A discharged battery condition no longer exists.'+

Since getting these messages we have fitted a replacement genuine new APC battery but we are still getting the messages. Here are some details displayed in the UPS software:

Input Voltage: 237.6 VAC
Output Voltage: 237.6 VAC
Runtime Remaining: 6 minutes
Last Battery Transfer: Due to software command or UPS's test control
Low Battery Duration: 02 minutes
Shutdown Delay: 090 seconds
Maximum Required Delay: 2 minutes

Any ideas why we keep getting the warnings?

Regards

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

well, there are a few ways we can do it. the software calibration will only discharge the UPS to between 10-20% so it will not turn off your load.

if you'd like to adjust the calibration setting via hyperterminal/serial connection, let me know. this requires the APC serial cable of 940-0024 or 940-1524. any other serial cable attached will most likely cause the UPS to drop the load since it has a special pinout.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

It is a new APC genuine battery. Would calibration power off attached equipment? Is it best done 'out of hours'?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

it sounds like you may need to calibrate the UPS and its battery since your runtime is only 6 minutes.

before i say that though, how much load is on your UPS? this alarm generally means that your reported runtime (6 minutes) is within 2 minutes of your low battery signaling time/low battery duration. thus, your load might be fluctuating a bit where the runtime is dropping and getting close to only 2 minutes, since your low battery duration is set to 2 minutes, according to the data you provided.

thus, please provide the percentage load on your UPS and then also, how much runtime do you normally get on battery?

you may also see a flashing battery bar graph if this is an older UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:27 AM

The Load on the UPS is 41.6 % (not flashing so i guess not that old πŸ˜‰
We used to have up to 7 minutes battery on the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:26 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:35 AM . Last Modified: β€Ž2024-03-13 03:26 AM

oh hm ok. so the 6 minutes is probably correct. via the data log on the UPS, is the load fluctuating a lot? to cause the runtime to go down a bit, closer to the 2 minute low battery duration? the alert is trying to tell you that your low battery time is close to your reported runtime so if the UPS goes to battery, everything will immediately shutdown.

what is the exact model of UPS? are you local to the unit? id like to reference the runtime chart since that UPS is not even fully loaded and it only gives you 7 minutes. seems a little low.. if you dont have the exact model, like SUA3000RMI2U, then does the UPS have an LCD screen on it or the LEDs I referenced?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

The exact model number is DLA3000RM12U and yes i am local to the unit. The load doesn't fluctuate really as the servers attached to the unit stay up at all times together. We do a power off test every two months which is the only event that changes the load on the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

0 Likes
0
1609
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

hmm, ok. i think you should get more than 7 minutes. i am looking at an old runtime chart for the APC Smart UPS 3000 of this model and at about 1100 watts, or 41% of its capacity, you should see more like 15 minutes.

i'd like to recommend we do a calibration on this new battery. is it an APC battery or third party battery?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

0 Likes
0
1610
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 02:36 AM . Last Modified: β€Ž2024-03-13 03:26 AM

well, there are a few ways we can do it. the software calibration will only discharge the UPS to between 10-20% so it will not turn off your load.

if you'd like to adjust the calibration setting via hyperterminal/serial connection, let me know. this requires the APC serial cable of 940-0024 or 940-1524. any other serial cable attached will most likely cause the UPS to drop the load since it has a special pinout.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.