Smart-UPS 2200 non-APC battery problem

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 non-APC battery problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

0 Likes
2
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:43 AM

Smart-UPS 2200 non-APC battery problem

Hello, all. Sorry if this is a bit long winded, but I really, really want to get this working. I spent a lot of time and gas and money getting this UPS.

I recently got my hands on a Smart-UPS 2200 with bad batteries. I took it home and promptly removed the connectors from the old batteries (after trying them in the UPS to no effect) and wired them to two Werker 12 volt 44 amp hour batteries. I know these batteries are good, as I have been cycling them on an older 600 VA APC UPS.

I plugged it in and pressed the "power/test" button. It powered up, and seemed to come on. Then it beeped a few times and the "Replace Battery" light came on. I powered it off, unplugged it, plugged it back in, and powered it up again. It did the same thing, the "Replace Battery" light came on. I pressed the "power/test" button and it seemed to go into the test mode, and all lights turned off except the bottom most "Battery Charge" light. I figured it was either doing it's test, or it was charging the batteries. So I watched it for a minute or two, then left.

I came back about 20 minutes later and saw that the bottom most "Battery Charge" light was still on. I pressed "power/test" button and the UPS turned on. The "On Line" light came on, the fan came on, and it seemed to be OK. I watched it for a couple minutes, and everything seemed good, so I left. After probably 20 minutes I heard a high pitched noise coming from where the UPS is. I raced down there, thinking it was some alarm, but when I got there I could tell it wasn't. The noise was coming from inside the UPS, and wasn't an alarm. I quickly unplugged the UPS and the noise slowly faded. I put a hand on the top of one of the batteries and it was hot, I put my hand on the side of the other battery and it was very, very hot. I could hear the water inside the batteries sizzling. I quickly unplugged the connectors from inside the UPS and checked the voltage on the batteries. One read 13.5 and the other 13.7.

So, my question is this: why did the UPS do that to the batteries? I wired the connectors exactly like the originals. The only differences between the originals and my new ones is that the originals were actually two packs of two six volt batteries, each pack wired in series to make 12 volts. My batteries would be the same 12 volts, but with a higher amp hour rating. This should work, but it didn't, and I don't know why.

Any help would be hugely appreciated. I wanted to use this for my file server, hardware firewall, and networking stuff, and it's a quite disappointing that it doesn't work.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
hkpolice_apc
Ensign hkpolice_apc
Ensign

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

0 Likes
0
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

You fried your batteries. The UPS requires 4x12v batteries in series for a total of 48v, you didn't do any research and just assumed that it took 2x12v batts. The UPS was charging the batts @ around 54-55v so most of the electrolyte has already gassed off and the lead inside the batteries could've melted, creating a short. If I were you I'd recycle the batteries and buy some proper sized replacements because charging them again will likely result in another overheat.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
hkpolice_apc
Ensign hkpolice_apc
Ensign

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

You fried your batteries. The UPS requires 4x12v batteries in series for a total of 48v, you didn't do any research and just assumed that it took 2x12v batts. The UPS was charging the batts @ around 54-55v so most of the electrolyte has already gassed off and the lead inside the batteries could've melted, creating a short. If I were you I'd recycle the batteries and buy some proper sized replacements because charging them again will likely result in another overheat.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

0 Likes
0
930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:09 AM . Last Modified: ‎2024-03-12 04:42 AM

Well, that sure answered that. I pried the two APC batteries apart and they are indeed 12v each. I assumed they were 6v because when I checked the voltage of one pack it read 12.5v, and the other pack read zero.

I'm going to check these two Werker batteries to see if I really did fry them, but you're probably right that they are no good anymore.

I will be getting four more Werker batteries because I can get them for free, and wire two in series for each pack like they should be. I have the room because I made a 36 inch deep server rack, so I just need a shelf that can hold all the weight.

Thanks for the information and help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore