The last two times when the UPS runs a self-test there has been an error afterwards.
Notifications go like this:
Does this mean that the self-test is wrong and the battery is starting to wear out?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:17 AM . Last Modified: 2024-03-15 05:59 AM
The battery is less than two years old. I created a support case and they will replace the battery under warranty.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:16 AM . Last Modified: 2024-03-15 05:59 AM
Hi Bartolo -
Either you have a very large load connected to the UPS, you have your low battery signal set very high (default is 2 minutes) or the battery is starting to wear out. When was the battery last replaced?
Liam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:17 AM . Last Modified: 2024-03-15 05:59 AM
The battery is less than two years old. I created a support case and they will replace the battery under warranty.