Smart-UPS 2200 battery problem
The last two times when the UPS runs a self-test there has been an error afterwards.
Notifications go like this:
- 0 seconds: self-test started
- 10 seconds: self-test passed
- + few more seconds: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
- + few more seconds: A discharged battery condition no longer exists.
Does this mean that the self-test is wrong and the battery is starting to wear out?
- Labels:
-
Smart-UPS & Symmetra LX | RM
- Tags:
- Smart-UPS2200
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:17 AM . Last Modified: 2024-03-15 05:59 AM
The battery is less than two years old. I created a support case and they will replace the battery under warranty.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:16 AM . Last Modified: 2024-03-15 05:59 AM
Hi Bartolo -
Either you have a very large load connected to the UPS, you have your low battery signal set very high (default is 2 minutes) or the battery is starting to wear out. When was the battery last replaced?
Liam
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:17 AM . Last Modified: 2024-03-15 05:59 AM
The battery is less than two years old. I created a support case and they will replace the battery under warranty.
Link copied. Please paste this link to share this article on your social media post.