Smart UPS 2200 (NEW!) not found - Failed to apply profile

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart UPS 2200 (NEW!) not found - Failed to apply profile
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
8
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Smart UPS 2200 (NEW!) not found - Failed to apply profile

Hello,

I recently replaced a faulty (aged) Smart UPS 1500 for a new Smart UPS 2200. The first day it was working fine. The next day the UPS was bleebing and communications were lost. I re-installed the software, but the UPS is not found. So I thought having a blue Monday product and replaced it for a new one again (including serial cable). But the new one is also not found. Deleted all PowerChute modules en re-installed (the latest) the software again. But during setup the UPS is not auto detected. I can fill in the required fields manually and selected COM1 and Smart UPS. The setup continues. Though when I configure the Console, I get: Failed to apply the configuration profile to SERVER.

The Server is a HP Proliant ML 350G6, OS=Windows Small Business Server 2008

I'm completelly lost. Any help is apriciated.

Best Regards

Dennis

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

As stated before, after connecting with an USB cable, I was able to configure/install the software. Also the configuration profile was applied correctly.

Thanks and Regards

Dennis

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

To start with, let us help you by gathering the information that we would need to assist you better.

We would like to know the exact model number of the UPS that you just bought. This is normally found at the back of the Smart-UPS where there is a small white barcoded sticker. Next, what kind of communication cable were you using? Is it USB or serial? Do you have the part number of the cable as well? You have mentioned that you've uninstalled and reinstalled an APC software, is it PowerChute Business Edition or Network Shutdown?

If you are using a USB connection, can you check the Device Manager and see if it is listed there.

Once we have all of these information, we would start digging more about your problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Hi JonPro,

As I'm not on the client site, I try to gather the information from my archive.

The model of the UPS = SMT2200I

The used cable is a serial cable, which was shipped with the UPS (and has been replaced as well). At the UPS site, a RJ45 connector and at the server site DB9. Don't know the exact partnumber.

The Software Used is PowerChute Business Edition v9.0.1.


Hope you can help.

Best Regards

Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Thanks for giving us an update. Basically, when you are using serial communication the UPS is not detected automatically by the PC. Have you tried this on a different PC or have used the USB cable to see if it gets detected?

I would also make sure that there are no services or programs that might be interfering with the serial port/communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Hi JonPro,

I connected the UPS via USB. I was not able to test the UPS on a different machine, as I had no machine with a comport avialable onsite. Via USB I was able to configure the UPS, install the software, well.
Maybe a faulty comport? I will try to confirm that, as the server is brand new and thus under warranty.

Thanks for your help!

Best Regards

Dennis.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Hi Dennis,

After installing PowerChute Business Edition, were you able to get to the web interface? If not, can you please open up a web browser and key in https://PCIPAddress:6547 this should open up the Agent interface. Make sure that your UPS is detected and it doesn't say something like Unknown Device. Also, during the installation of PCBE Agent and Server it asked you to key in your desired username and password and this should have the same value.

Also, kindly check this APC Knowledgebase Article - ["Failed to Apply Configuration Profile" error when adding Agents to PowerChute Business Edition Server|http://nam-en.apc.com/app/answers/detail/a_id/2596/kw/failed%20to%20apply]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Hi JonPro,

The web interface works correct. Though I knew about the username issue. Still believe it's a faulty comport.

Thanks for your help.

Best Regards

Dennis.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

Hi Dennis,

If the web interface works fine, meaning it detects what kind of UPS is attached to it it means that they are communicating with one another. If it is the Failed To Apply the configuration profile that you are experiencing, then the APC KBase should give you an idea on what should be checked.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

0 Likes
0
1348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:42 AM . Last Modified: ‎2024-03-08 05:03 AM

As stated before, after connecting with an USB cable, I was able to configure/install the software. Also the configuration profile was applied correctly.

Thanks and Regards

Dennis

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore