Smart-UPS 2200 High Battery Temp

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 2200 High Battery Temp
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
NotJerry
NotJerry
Cadet

Posted: ‎2025-04-11 08:59 PM

0 Likes
4
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-11 08:59 PM

Smart-UPS 2200 High Battery Temp

Got a Smart-UPS 2200 (SMT2200R2X658) I purchased off Newegg refurbished.

I have the UPS in my 32U cabinet in a room that's around 68F.

 

I purchased a management card and noticed my battery temp reading is 58.9°C, I checked the main display and it shows the same. My racks temp sensor below the exhaust fans is reading 21F, which is around the 68-70F ambient room temp. I felt the air coming out the back below the management card and its cool, I touched the top of the UPS and its cold.

 

If the batteries were really 140F I would think the top of the UPS wouldn't be cold. Anything I should try?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Teken
Kirk Teken
Kirk

Posted: ‎2025-04-14 03:16 AM

0 Likes
0
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-14 03:16 AM

Show me the following logs from the NMC: Data, Event, UPS. Remove the battery cartridge and measure the outside temperature of the housing from multiple sides and report back the results.

 

Open up the case and visually & physically inspect every cell. Assuming the internal sensor isn’t faulty you’ll probably find one or more cells bulging, warping, venting.

 

Take a photo of all the cells along with the production sticker vs what the system indicates is the battery installation date and report back.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

NotJerry
NotJerry
Cadet

Posted: ‎2025-04-14 08:14 PM

0 Likes
0
925
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-14 08:14 PM

Here are the 3 logs. I was eventually going to ask NationalGrid about the input spikes, some of them were 130-132vAC input.

 

I will have to wait till Wednesday for me to pull the cartridge and take temps with my FLIR, I have a webserver I will need to schedule downtime on.

 

While I will have it apart, does SE have a ohm/temp table somewhere for the sensors? That, or a parts list.

 

Thanks!

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

NotJerry
NotJerry
Cadet

Posted: ‎2025-04-15 11:58 AM

0 Likes
1
900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-15 11:58 AM

I did pull the cartridge out real quick and pulled the top cover, everything was at 70F and looked ok visually. I used my thermal camera inside the cartridge slot and saw no high temperature, the sensor in the back looks ok and is still ziptied in place.

 

I will have to pull the cartridge back out tomorrow for the production sticker. The battery installation date was May last year as I got the UPS and cartridge in 2 separate shipments, so I had entered in the battery install date when I put it in the cabinet.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-04-16 01:15 AM

In response to NotJerry
0 Likes
0
899
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-04-16 01:15 AM

When you take a picture of the battery production sticker. Leave the cartridge out for about 30 minutes and than show me the event, data logs.

 

My expectations is the internal temperature will drop but would like to see if it mimics the ambient room temperature at some point.

 

I would take a small fan and place it in front of the opening to speed up the cooling process.

 

If after 30 minutes the internal temperature is still above the room’s ambient temperature than the sensor may very well be defective. 

I would recommend you take the top cover off the unit to visually inspect the entire compartment is clean and free of any debris. Take the thermal camera and validate no single component is faulty or beginning to fail.

 

Based on the information you provided the unit is 11 years old. The useful service life of the system is approximately 7-10 years as such expect component failure some where.

 

https://www.apc.com/us/en/faqs/FAQ000265093/

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore