Smart-UPS 1500 unknown problem
Hi,
My Smart-UPS 1500 (sua1500rmi2u) has 3 orange and 2 red leds blinking (without beeps or sound).
- Labels:
-
Smart-UPS & Symmetra LX | RM
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
Hi Salvatore,
As to what Bill has posted before, if the LEDs won't go back to normal after following the steps that he has recommended and it is still producing the same behavior then the UPS should now be replaced.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:02 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:02 AM
Is the sentitivy set to High Or Med?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:02 AM
On 10/29/2016 6:45 PM, john said:Is the sentitivy set to High Or Med?
It was High. I already try to set it to medium but the problem persists.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
On 10/29/2016 10:37 PM, Valerio said:I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
I'll will try tomorrow.
Shutdown the UPS, disconnect from power and again press 0 to disconnect Battery power doesn't work. I'll try to disconnect the battery.
It's strange that all works and Powerchute reports that everything works. But leds are blinking...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
On 10/29/2016 10:37 PM, Valerio said:I've been able to solve some weird behaviours by disconnecting the ups from supply and then disconnect the battery. Wait some minutes and then reconnect the battery and plug into mains.
Hope it'll help
i tried to disconnect the battery but leds are blinking yet.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
Hi,
Try this reset procedure
1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back on
If this does not resolve the issue then there is an internal fault and the UPS will need to be replaced.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
On 10/31/2016 2:06 PM, Bill said:Hi,
Try this reset procedure
1) Turn off and unplug UPS from wall
2) Press and hold the OFF button again
3) You may see a quick flash of the LED's and you should hear an audible "click" from the UPS.
4) Plug UPS back into the wall and turn UPS back onIf this does not resolve the issue then there is an internal fault and the UPS will need to be replaced.
after procedure leds are blinking yet. But why powerchute reports that's all fine and all work fine? Thanks in advance.
S.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
You just did a question that any answer this is usable by a very experienced electronics engineer and also specialist in electronics repairs.
Sort explanation this is inside components aging issues including capacitors and electrical relay.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 09:01 PM . Last Modified: 2024-03-07 12:01 AM
Hi Salvatore,
As to what Bill has posted before, if the LEDs won't go back to normal after following the steps that he has recommended and it is still producing the same behavior then the UPS should now be replaced.
Link copied. Please paste this link to share this article on your social media post.