Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
I have a Smart-UPS 1500. After i do a battery replacement. The status at the battery bar still show no charging and always blinking... i also had do the self test and also disconnect the battery and direct on the UPS but the UPS still cant on ... Is that mean the UPS also faulty already??
pls Help if anyone hav face this problem before...
thanks
Message was edited by: alex0120
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Alex,
I am not sure if I understood this question..+APC have sell UPS withouth battery?+ Could you please explain?
And also let us know the exact Model and Serial number of the UPS. You can find these details on a white bar code sticker at the rear of the unit. Did you perform the manual runtime calibration as Instructed above? If so, are the battery bar lights still flashing?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Alex,
I would recommend that you to perform a manual runtime calibration because sometimes after replacing the old batteries in the Smart UPS, the device needs to be told that there are new batteries present and even after replacement the UPS still assume the characteristics of the old battery.
You can find the manual runtime calibration instructions here.
I hope that this helps.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Hi techie,
thank for your help. i have one more question. If i had tested to power on the UPS without the battery but cant on . Is that mean the ups faulty also ? i want to make confirmd about this.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
If all plug well..is that mean the UPS faulty?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
APC Smart UPS SUA series UPS should come online when it is plugged in even without the battery attached. Please be sure that the UPS is receiving normal AC Power from the wall when you try to power on it without the battery.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
hmm...If the UPS does not come online when there is power from the wall without the battery, then there should be something wrong the UPS circuitry. In this case, the Smart UPS SUAXX UPS should come online and indicate flashing Replace Battery Light if the battery is not connected.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
thank...
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
APC have sell UPS withouth battery?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:00 PM . Last Modified: 2024-03-14 03:49 AM
Alex,
I am not sure if I understood this question..+APC have sell UPS withouth battery?+ Could you please explain?
And also let us know the exact Model and Serial number of the UPS. You can find these details on a white bar code sticker at the rear of the unit. Did you perform the manual runtime calibration as Instructed above? If so, are the battery bar lights still flashing?
Link copied. Please paste this link to share this article on your social media post.