Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Smart-UPS 1500 behind Photvoltaik UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 behind Photvoltaik UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
139
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
quaker
Crewman quaker
Crewman

Posted: ‎2025-01-07 06:00 AM

0 Likes
7
2087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-07 06:00 AM

Smart-UPS 1500 behind Photvoltaik UPS

Hi all,

 

I have a Smart-UPS 1500 that has generally worked flawlessly until we installed a photovoltaic system with a battery storage unit. The PV storage switches seamlessly in the event of a power outage, and everything runs as it should. However, ever since the power comes back on, the Smart-UPS 1500 briefly switches off and then back on. As a result, my server shuts down. What could be causing this behavior, and is there a way to fix it?

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2025-01-08 08:44 AM

0 Likes
2
2059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-08 08:44 AM

You’ll need to provide the following information such as the event, data, ups logs.

 

Provide the exact model UPS, serial number, UPS ID & Firmware installed.

 

Show me a clear photo of the back output (outlets) of the rear of the system. Provide an image capture of all the settings relating to power quality for the UPS. 


Lastly, show me the battery installation date and the production sticker on the cartridge. If the UPS system is connected to a server and has APC Power Chute software disconnect the USB cable.

 

If there is another power blip report back how the system behaves without the USB cable connected to the server. ☝️

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

quaker
Crewman quaker
Crewman

Posted: ‎2025-01-15 03:59 AM

In response to Teken
0 Likes
1
1997
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-15 03:59 AM

sorry for delay. Here are the requested information.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-01-15 07:48 AM

In response to quaker
0 Likes
0
1986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-15 07:48 AM

Please indicate the model, serial number, UPS ID (Firmware). Battery installation date, battery production sticker.

 

Has the USB cable been disconnected from the computer running PCSS?!? If so has there been any problems where the power blipped and the UPS behaved improperly?

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

quaker
Crewman quaker
Crewman

Posted: ‎2025-01-16 01:48 AM

0 Likes
1
1959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-16 01:48 AM

USV-Modell: Smart-UPS 1500
Seriennummer: AS1712151498
Firmwareversion: UPS 09.3 / MCU 19.0 (18 - 19)

Battery installation date 03/2019

 

battery production sticker. -> where to find?

 

Has the USB cable been disconnected from the computer running PCSS?!? If so has there been any problems where the power blipped and the UPS behaved improperly?

 

No, not yet. But at the meoment no power cut off happend.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-01-16 04:21 AM

In response to quaker
0 Likes
0
1949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-16 04:21 AM

Assuming you have never changed out the battery cartridge. Based on the information you have provided the battery cartridge is six years old.

 

The average service life of the battery cartridge is 2-5 years based on usage, temperature, and environmental conditions.

 

You’ll need to perform a static & dynamic load test of the system to gauge how the system performs.

 

Static: Remove all connected loads from the outputs. Disconnect AC Mains from the wall and time how long the unit runs.

 

Dynamic: Ideally you would have the same connected loads such as your servers connected. But you may replace them with anything such as a fan, heater, etc.

 

Remove AC Mains from the unit and time how long the system operates for and compare it to the APC Runtime Calculator.

 

There will be three possible outcomes for the two tests. Immediate shutdown, very short runtime, to average runtime when compared to a new battery cartridge.

 

Report back what you see and observe upon completing both static & dynamic load tests. 


NOTE: The battery production date is either stamped (silkscreened) or identified by a alphanumeric sticker that is white / white-yellow.

 

Questions Ask . . .  👍

Reply

Link copied. Please paste this link to share this article on your social media post.

quaker
Crewman quaker
Crewman

Posted: ‎2025-01-23 01:22 AM

0 Likes
1
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-23 01:22 AM

Hi, test done, removed Main power and testet runtime with complete load.

runtime with load ~20mins

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-01-23 03:20 AM

In response to quaker
0 Likes
0
1887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-23 03:20 AM

Leave the USB cable disconnected from the two systems. Report back once there is a power outage and what you see and observe.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore