Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:15 AM

0 Likes
4
1891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:15 AM

Smart-UPS 1500 XLM aka SUM1500RMXLI2U overload problem with no load....

Hi, i'm new to ups diagnostics 🙂 and this is my first problem. I will try to explain the problem brief but complete and supply with enough information.

The ups has been bought 2nd hand as a try-out for my new home business. It has feeded my dual socket server for almost a year. It has a date of 2006 and the original batteries are still being used (see pictures). I don't mind replacing the batteries ..... if that is needed to be done.

problem: It does not start. If i power the ups, it will start with the self test. Here the "online" led will go on first, followed by a blinking "on battery" led going over to a red non-blinking "overload" led with a disgusting background sound. So i switch it of to stop the sound. The ups is partly on but no green lights. he 2 fans are on and i can connect to the ups hence the supplied pictures. No hardware is connected to the ups , so no load....

i tried: brain dead option, removed the battery connection inside and connected again, nothing helped.

Info:
ups model: smart-ups 1500 xlm
serial number: QS0645320159
manufacture date: 23-9-2006
firmware rev: 716.3.1
battery replaced: 23-9-2006

ups status: unknown
internal temp: 24,7 C / 76,5 F
output voltage: 0 vac
input voltage: 227,5 vac
output freq: 50 hz
load power: 3,9 % va
load current: 0 A

battery status: Normal
battery voltage: 54,54 VDC
Runtime remaining: 205 min
battery replaced: 23-9-2006
battery pack count: 0
battery charge: 99%


ups self-test
last self test: 4-9-2012
result: failed

ups-calibration: unable to do this...
cal. date: unknown
cal. result: unknown


Can someone help me diagnose the problem?
Is there something like a fuse?
Thanks in advance...

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc
  • battery
  • beeping
  • dead
  • hardware
  • overload
  • overloading
  • power
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

The XLM model allows removal of the inverter/charger/controller module (right side of ups om rack mount orientation) ....if you remove the screws on the front (philips screwdriver) flip over the little tab lever at the bottom left you can pull out the module. Have you tried that step to refresh the electrical connections between the module and the ups cabinet (frame) ?

Message was edited by: Battman

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

Hi! Are you sure that its the Overload LED that's lit? Because if it is, it may indicate an internal fault (that is if there is no load attached). If it's not, and it is the Replace Battery LED (the one that looks like a battery with an "X" inside it) that is lit solid and accompanied by rapid beeping after the selftest then it's just the batteries that need to be replaced.
[You can get the batteries here|http://www.apc.com/tools/upgrade_selector/index.cfm]

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

also, are you using both powerchute business edition AND a network management card? i ask because you are showing screenshots of the PCBE interfaces and then you show a screenshot of putty which is a network management card screen (since this UPS comes pre-installed with one). you should only be using one or the other technically so if I had to suggest one, it should be the network management card.

I would disconnect the serial cable and either terminal in or web in to the network management card to set it up and i need to review the logs in there which would be extremely helpful in diagnosing this issue with you.

here are some knowledge base articles to help you:

• How to set up the network management card with an IP address: http://www.apc.com/support/index?page=content&id=FA156064

• How to download the event.txt, data.txt, and config.ini (which I'd like to see - feel free to remove any private info): http://www.apc.com/support/index?page=content&id=FA156131

if you can post those logs here, it should help greatly.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

0 Likes
0
1889
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

ok, thanks for the replies.

I will see into the logs and post them. The link you supplied is down currently ... i have to wait.

Yes, the overload led is on. And also now the Bypass led is on together.......

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

0 Likes
0
1890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:05 AM . Last Modified: ‎2024-03-11 03:14 AM

The XLM model allows removal of the inverter/charger/controller module (right side of ups om rack mount orientation) ....if you remove the screws on the front (philips screwdriver) flip over the little tab lever at the bottom left you can pull out the module. Have you tried that step to refresh the electrical connections between the module and the ups cabinet (frame) ?

Message was edited by: Battman

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of